Fireproof Cabling Security #453472 01/26/10 11:55 AM
Joined: Apr 2004
Posts: 586
jjimm Offline OP
Member
OP Offline
Member
Joined: Apr 2004
Posts: 586
I am cabling an old 6 story hotel and intend to use plenum cat 5e to make it fireproof. The customer wants to make the cabling tamper-proof. I am looking for a fire-proof,low-cost alternative to steel conduit. Most raceways are PVC and "fire-retardant". This means they burn at temps above, say 95 degrees, and when they burn they give off toxic gas. So I am thinking this would make my fireproof cable illegal for the firecode. I want to be safe and not have to redo the whole job if inspected. I will have about 10 cables per floor side, requiring 3/4" diameter (I think) feeding to a box that feeds 3 individual rooms. Anyone have any low-cost fireproof suggestions?

I can't find anyone that knows specifically what the fire codes are for telephone cabling or enclosures in the San Francisco area. Does anyone know?

Telephone Equipment Search
Re: Fireproof Cabling Security #453473 01/26/10 02:30 PM
Joined: Feb 2005
Posts: 11,986
hbiss Offline
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 11,986
Last question first. The AHJ or electrical inspector is the person to talk to BEFORE you plan this job since you have no clue.

As for the use of PVC, that would be up to the local codes which the AHJ or inspector will fill you in on. It is NOT fire retardant and neither is a plenum listed cable. They WILL burn but just not give off as much smoke as a non-plenum cable. So don't call them "fireproof"!

If it were me I would run everything in EMT and save money by not using a plenum listed cable and CAT5e.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Re: Fireproof Cabling Security #453474 01/26/10 04:31 PM
Joined: Nov 2009
Posts: 237
ampleworks Offline
Member
Offline
Member
Joined: Nov 2009
Posts: 237
Hal's right. EMT with standard riser cable rather than plenum. Anything you're going to find that doesn't give off toxic fumes is going to cost a heck of a lot more than EMT.

While you're at it running the feeders, I would go 1" with ten cables just in the event that you need to fish another one at a later date. That many in 3/4" is going to be pretty tight.


Jeff
Lead Field Engineer, MSCNS
Re: Fireproof Cabling Security #453475 01/26/10 05:23 PM
Joined: Jun 2006
Posts: 8,389
MooreTel Online Content
Moderator-Nortel, Computers, General
*****
Online Content
Moderator-Nortel, Computers, General
*****
Joined: Jun 2006
Posts: 8,389
I have to agree with the above. For the EMT, the larger the better. Words of experience.


Scientists say that the universe is made up of Protons, Neutron & Electrons. They forgot "Morons".
Dave. (CTUB) Canadian Techs Use Bix!
Re: Fireproof Cabling Security #453476 01/26/10 09:24 PM
Joined: Apr 2004
Posts: 586
jjimm Offline OP
Member
OP Offline
Member
Joined: Apr 2004
Posts: 586
Installing conduit might mean losing the job after funds are spent.I'm the one was concerned about "fireproofing"-Since I've never worked a job of this size, I want to be sure I'm not liable.
I did find some specs on SF wiring online-
https://www.archive.org/stream/gov.ca.sf.electrical/ca_sf_electrical#page/n21/mode/2up

According to this, anything lower than 50 volts need not be enclosed in metal raceways, tubing, or wireways. I certainly would like to ask an authority. But,I've never had to work w an electrical inspector for low voltage telephone cabling. Is the HV electrical inspector the AHJ for low voltage? Should I talk to a fire inspector as well?

Re: Fireproof Cabling Security #453477 01/27/10 04:24 AM
Joined: Nov 2009
Posts: 237
ampleworks Offline
Member
Offline
Member
Joined: Nov 2009
Posts: 237
Even using something like metallic Wiremold you're looking at approximately 5-7 times the cost versus EMT.

Is this all to be surface mounted or some in drop ceiling/hard ceiling?


Jeff
Lead Field Engineer, MSCNS
Re: Fireproof Cabling Security #453478 01/27/10 06:52 AM
Joined: Feb 2005
Posts: 11,986
hbiss Offline
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 11,986
Yes, the electrical inspector is the electrical inspector. Point here is some jurisdictions will not allow the use of PVC pipe or conduit and that can be based on the occupancy. The electrical inspector would certainly know and I would talk to the building inspector also. And as long as you are talking to city hall I would check to see if a permit is required as well as an inspection. Might as well get this all cleared up before hand so you can decide if you want to do this.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Re: Fireproof Cabling Security #453479 01/27/10 10:05 AM
Joined: Feb 2009
Posts: 2,952
MnDave Offline
Moderator-Vodavi, Vertical, XBlue
*****
Offline
Moderator-Vodavi, Vertical, XBlue
*****
Joined: Feb 2009
Posts: 2,952
40% conduit fill is the NEC code but local codes may differ. Also, be careful to never use the term "fireproof". Plenum cable burns but just doesn't give off the same level of toxic fumes. Most fatalities in a fire are from smoke inhalation.


- Dave S. -

You can never appease your ideologue opponents.

Re: Fireproof Cabling Security #453480 01/27/10 11:18 AM
Joined: Apr 2004
Posts: 586
jjimm Offline OP
Member
OP Offline
Member
Joined: Apr 2004
Posts: 586
To tamperproof the cable it only needs to be protected (covered) from the IDF to fdr can (3 cables) = 15 ft and from the fdr can to the room (1 cable)= 6 to 15 ft each room. I was thinking about covering the plenum cables with metal "C"-shaped rods. Or-sub out the conduit work to a electrical contractor.

Of course the customer is pushing for the estimate and says he will lose funds if estimate not in by Feb. By the time an electrical inspector gets out there it will be weeks (months?) before he gets there. I'll find out today. Also, I need to ask customer permission-I don't want to be a whistle-blower- there are phone cables run out windows and down 5 stories in all the air spaces,exposed cruddy wires along hall ceilings, new security cameras installed w cat 5 and baluns using PVC and covered w PVC raceway in some places run alongside the telco cables, and new coax CATV neatly running down the air shaft. The only thing in conduit is the new HVAC (neatly done)= I would guess it cost $100k+ for the HVAC job alone and that's what customer wants to avoid..

I feel confident the plenum cable exposed should be ok and I don't see any problem giving customer an estimate for that at this point plus an estimate on PVC cable if he has conduit installed

At this point, I'll call customer to get permission to call city hall electrical inspector and call a sub to estimate cost on the conduit from IDF to rooms.

What do you think?

Re: Fireproof Cabling Security #453481 01/27/10 11:34 AM
Joined: Apr 2004
Posts: 586
jjimm Offline OP
Member
OP Offline
Member
Joined: Apr 2004
Posts: 586
Just getting a job like this is a Godsend at this bad economy time. In better times I would just define my boundaries-I'll do PVC cables, electrical contractors install conduit and we'll do install afterward. But at this point in time, I've had to stretch my borders- used to be my company did phone systems, VM, paging & PAs and small networks. Now it's anything low voltage- add security cameras, computer programming and troubleshooting, CATV, and anything else low voltage.

This job is certainly bigger than my normal job size, but it's been good profit here and looks like a great opportunity. The security added is an issue we all will face, as is the low-cost alternatives.

I'm not doing business "as usual" in this economy and have made some adjustments= stretching technical boundaries, doing flat rates instead of T&M, and more negotiation. This job is a good example for defining or stretching boundarie

Page 1 of 2 1 2

Moderated by  Professor Shadow, Silversam 

ShoutChat Box
Comment Guidelines: Do post respectful and insightful comments. Don't flame, hate, spam.
Most Recent 5 Post
DS2000 One Line goes direct to a mailbox
by Randy - 12/11/19 04:53 PM
NS1000 license question
by conxtel - 12/11/19 04:47 PM
Getting out of the biz after 20+ years!
by breeze - 12/11/19 04:28 PM
SBX voicemail problem
by davescomm - 12/11/19 03:24 PM
sts ogm volume
by davetel - 12/11/19 02:52 AM
Who's Online Now
60 registered members (Carl Navarro, davescomm, Curlycord, usedphones, jeffmoss26, BobRobert, Southernphoneman, 1864, justbill, mreilly, MikeChu, nortelvoip, RATHER BE FISHING, brokeda, Mercenary Roadie, Yoda, gelehu, Joe Talbot, dexman, Bob3470, Coral Tech, ffej010, Professor Shadow, Ted, OBT, dans, Arthur P. Bloom, metelcom, www.telcom1.net, Casey Y, adteldon, jknichols, Touch Tone Tommy, Ruben, STS E, tmeier, newtecky, breeze, srg, BTS01, Daniel, KRRath, RobertTBS, Randy, andyphones, Meyery2k, nonameyet, conxtel, jmrj65, Silversam, Fosnut, MooreTel, vicbob, helpifican, jab1780, RM SYSTEMS, jmesi, JBean3329, Skunky, ItsStuart), 1,782 guests, and 497 spiders.
Key: Admin, Global Mod, Mod
Tech Support Line 1.800.766.3425
Over the Phone Tech Support for your Phones and Business Phone Systems
Popular Topics(Views)
Forum Statistics
Forums62
Topics93,087
Posts633,087
Members49,189
Most Online5,661
May 23rd, 2018
Today's Birthdays
acclaimpc, aregowe, commgeek, fxsfxo, jmarc, Lazy J, telcomgal
NEC DX-40 PKG $299
NEC DX-40 PKG $299
EMP & Lightning Home Surge Protection
EMP - Click Here!
Top Posters(30 Days)
dexman 13
dans 10
Daniel 8
RedBul 8
POLYCOM SOUNDPOINT 10 Pack
FREE Voip Phone - Click Here!
50% OFF Most All Phones
FREE Voip Phone - Click Here!
RESPONSIVE WEBSITE DEVELOPMENT
Bluewater Sailing
Become a Patron! https://www.patreon.com/bePatron?u=5256033
Free Phone Repair Diagnostic
EMP Shield for Commercial - Home & Vehicle
Use Coupon code SAVE - Click Here!
Servpro Ventura 24-Hour Emergency Service
Free Estimates call us now 24Hours
Contact Us | Telephone System Tech Support | Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers.
©Copyright Sundance Communications 1998-2019
Trusted Partners