have a 200 series contoller rev c cpu is a 21-0260-00 rev c, and backplane is 21-0261-00 rev b, I have one door off of system that they want a key switch control to disable, it has a maglock on door, is the best way a switch to disable 12/24 maglock? is anybody familiar with this set-up?

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#479388 07/07/06 02:18 AM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
What we normally do is call in a locksmith to change the lockset to a keyed barrel. When they want free acess to the door, simply unlock the handle (and leave it unlocked) with a key.

That controller also has the ability to program in schedules for free access, but if you want to control it non-time dependent, use a keyed lockset.

#479389 07/07/06 02:23 AM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
Sorry, I just reread your post, it's a maglock, not an electric strike.

Yes, you could install a keyswitch on the mag to cut the power or a programmed schedule.

I'm not familiar with the series 200 and it appears it is discontinued. Some software has the ability to program in a latching sequence. For example, a certain swipe card/tag would unlock the mag and leave it unlocked until that card/tag is used again.

#479390 07/07/06 01:19 PM
Joined: Apr 2006
Posts: 2,039
Member
Offline
Member
Joined: Apr 2006
Posts: 2,039
When you say "off of the system", does that mean it is NOT controlled by the controller?

If that's the case then you may get a shunt lock to bypass the mag lock. Even if the door is "In" the system a shunt may be used but this defeats the purpose of the system in the first place.

#479391 07/10/06 01:33 PM
Joined: Jan 2006
Posts: 312
Member
OP Offline
Member
Joined: Jan 2006
Posts: 312
apreciate the responses, The customer is a hospital that locks down a door except for a proxy reader or keypad that releases a maglock & uses a horton automatic door opener to open the double doors if someone either: hits the press to egress button from the inside, has a proxy device , or enters a code. they would like to have a key switch located at the nurses station for manually unlocking door(maglock) at various times of the day(cannot schedule open)It should be a make break to the maglock. if my thinking is right , mostly do phone systems so need a little confirmation that I am thinbking correctly, a lot of great minds on this site, thanks in advance

#479392 07/10/06 02:01 PM
Joined: Dec 2005
Posts: 2,928
Member
Offline
Member
Joined: Dec 2005
Posts: 2,928
can you use a normally open keyswith connected to the RTE(request to exit)? When you tur the key it closes the contact and trips the RTE. a I am not familer with your conroller so I am not sure if it can be done.

have yo contacted Galexy control, they shoudlk be able to provide something for their syste, their tech support number:
800-445-5560

well at least that is what their website states

good luck


I Swear I did not touch anything bash
#479393 07/10/06 05:13 PM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
Most RTE use a built in timer control to release the mag. A maintained switch installed on this line probably will not work (once the time expires, the mag re-locks). Besides that, you would not want to keep that door opener energized, as it will burn out.

Foneman69 has the right idea. Just install the key switch in the mag power line. I'm not sure how far away the nurse's station is, but keep in mind line loss. You will have to use the appropriate wire gauge to compensate for this (Mag locks draw a bit of current and if they are starved, they will operate but weaker).

Even better would be if they allow you to mount that switch next to the door. If they insist on the nurse's station, and it's a fair distance away, you may have to use a relay.

#479394 07/10/06 11:51 PM
Joined: Dec 2005
Posts: 2,928
Member
Offline
Member
Joined: Dec 2005
Posts: 2,928
I got ya..I did not relize they want it open all the time, I thought the switch was just being used as an aditional exit means...now that I think about it that does not make much sense..sorry It was kind of a long weekend.....This being the case I agree a keyswitch on the mag side should handle this.


I Swear I did not touch anything bash
#479395 07/13/06 11:42 AM
Joined: Jan 2006
Posts: 312
Member
OP Offline
Member
Joined: Jan 2006
Posts: 312
So anybody know a type or part number of the key switch, I know that is a pathetic question but hey I'm a phoneman, that also does security cameras & access control, never really use key switches I think I could drill & mount it in the Horton controller above the mag lock, not going to hurt a nurse to walk to the end of the hall twice a day, maybe they will even check on a patient while they are up...

#479396 07/13/06 01:50 PM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
https://www.alarmcontrols.com/
Click on "Our Products."

If you just want a barrel lock, click on "Switches." Use the KA-107.

If you would rather mount it in the door mullion, click on "Remote Plates" and they have stainless steel narrow plates precut with the "D" hole for the lock. You can also have a status LED that you can wire up so they visually know the mag is energized.

Third option would be "cylinder stations." The advantage to this full size barrel is that you can have a locksmith key it the same as other locks (like a master key system).

Remember, you need to order a "maintained" lock (on/off), not "momentary."

These are available at ADI or TriEd.


Moderated by  metelcom 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,284
Posts638,772
Members49,765
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,459 Shoretel
188,321 CTX100 install
187,092 1a2 system
Newest Members
Nadisale, andreww, gohunt, Darrick, telecopippo
49,764 Registered Users
Top Posters(30 Days)
Toner 23
teleco 5
jc2it 4
dans 3
Who's Online Now
0 members (), 172 guests, and 389 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5