Look no further than the APC. It is either defective or it is too small to sustain power to the system for a reasonable amount of time.

Emergency generators take some time to come up to full load. The better ones get the engine and generator full up before cutting the power through the transfer switch. In that time period which can be several seconds to several minutes, the UPS needs to be able to fully power the system until the generator takes on the load.

In the city, we have several clients that will call, from time to time, and alert us to a planned power outage. When that outage is for a prolonged period of time, beyond what the UPS can sustain, we dispatch a technician and power down the system. When the power is restored, we send the tech to power the system back up again. We have never had a client complain or not pay the bill. It's just good insurance.

The electrician has no obligation to go to every electrical device and power it down. That's the owner's responsibility. You should have been notified by the owner of the planned outage and then you could have dispatched and powered down the system. The electrician had to power down the entire building or, at least, the part that your telephone system was connected. The emergency generator transfer switch has to be between the commercial power and the load for the generator to work. That involves a planned power interruption.

Rcaman


Americom, Inc.
Where The Art And Science Of Communications Meet
Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Dec 2005
Posts: 9,162
Likes: 8
Spam Hunter
*****
Offline
Spam Hunter
*****
Joined: Dec 2005
Posts: 9,162
Likes: 8
While not practical in a typical commercial setting, Central Offices will have battery strings that will support the present load while the site generator fires up and the transfer switch shifts from commercial to local power.


I Love FEATURE 00
Joined: Feb 2006
Posts: 1,716
Member
***
Offline
Member
***
Joined: Feb 2006
Posts: 1,716
In the old panel and SxS COs, the entire office was run on battery all the time. The commercial power was just used to keep the rectifier chargers going. It never made a difference if commercial power was available or not, the Bell Telephones ALWAYS worked!

Rcaman


Americom, Inc.
Where The Art And Science Of Communications Meet
Joined: Dec 2005
Posts: 9,162
Likes: 8
Spam Hunter
*****
Offline
Spam Hunter
*****
Joined: Dec 2005
Posts: 9,162
Likes: 8
Modern C.O. facilities are still operating that way. Offices can run on batteries for a period of time. Of course that isn't a situation that any provider wants to have happen.

Joined: Mar 2004
Posts: 488
Member
Offline
Member
Joined: Mar 2004
Posts: 488
This maybe be a litte unrelated. A few years ago when Starbucks opened in town. They had issue to get the utility power hooked up. They started to set up the store when running on a generator. The frequency was set incorretly instead of 60 HZ it was set for 100 HZ as a result the store had lotsa stuff that didnt like it. They had to replace a bunch of the electronic's.

Joined: Jun 2004
Posts: 399
Member
Offline
Member
Joined: Jun 2004
Posts: 399
Originally Posted by phoneguywayne
The frequency was set incorretly instead of 60 HZ it was set for 100 HZ as a result the store had lotsa stuff that didnt like it. They had to replace a bunch of the electronic's.
LOL, I thought you were going to say that all the clocks were running fast - and they were clocking out in 5 hours for an 8 hour shift!

Joined: Feb 2006
Posts: 1,716
Member
***
Offline
Member
***
Joined: Feb 2006
Posts: 1,716
This is why it's important to have a good generator with frequency and voltage meters to allow monitoring of the supply. There's a lot of room to go cheap, but this is not one of them. Expensive does not necessarily mean better, but in the world of generators, it usually does.

Rcaman


Americom, Inc.
Where The Art And Science Of Communications Meet
Joined: Nov 2006
Posts: 704
Member
OP Offline
Member
Joined: Nov 2006
Posts: 704
Thanks for all the info , very good help, already informed the customer for future reference. Will update apc ups. Much appreciated.

Joined: Nov 2001
Posts: 1,640
Moderator-NEC
*****
Offline
Moderator-NEC
*****
Joined: Nov 2001
Posts: 1,640
Not all UPSs have AVR. (automatic voltage regulation)

Cheaper ones don't kick in till the power is out and they will pass through low and high voltages.

Joined: Jan 2013
Posts: 519
Likes: 1
Member
Offline
Member
Joined: Jan 2013
Posts: 519
Likes: 1
When they installed the generator, they had to also install a transfer switch which means they had to kill the power to the building.

I'm willing to bet they didn't turn off everything, like your phone system and it had to go to the UPS.

Like everyone else said, UPS was probably bad or on the edge of being bad. When I was taking care of Fire Alarms at a school District, I got into the habit of testing everything that was battery backed up once a year and replaced the batteries every 5 years.

I have seen way too many UPS units that have never been touched since they were installed and many were so overloaded they would never of worked correctly even if new.

Page 2 of 4 1 2 3 4

Moderated by  MooreTel 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,262
Posts638,693
Members49,757
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,098 Shoretel
187,703 CTX100 install
186,792 1a2 system
Newest Members
BPopilek, Rich F, LewisR, TDKs79, Buttinset
49,757 Registered Users
Top Posters(30 Days)
dexman 18
Toner 14
TDKs79 8
Who's Online Now
1 members (Curlycord), 107 guests, and 246 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5