#618671 04/09/18 11:38 AM
Joined: Aug 2012
Posts: 71
grich Offline OP
Member
OP Offline
Member
Joined: Aug 2012
Posts: 71
Existing client has a tower site in the country, that's never had telco service. It was needed, so the telco buried 3000 feet of cable from the SLIC, along the road through the farmer's field and to the building.

Nice shiny new NID. I noticed there was no attempt to bond the NID to the building ground...the cable shield was attached to the ground terminal in the NID, but that's all.

Do you guys see this often?

I might give the guy a break because it's a thermobond building, and as it turns out, the main ground bar is at the far side of the building.

I went ahead and bonded it properly, because I didn't want to leave that hanging unbonded next to a 400' tall lightning rod.

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

grich #618674 04/09/18 12:20 PM
Joined: Feb 2005
Posts: 12,342
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,342
Likes: 3
What's a thermobond building? How did you "properly" bond the NID?

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
hbiss #618677 04/09/18 01:53 PM
Joined: Aug 2012
Posts: 71
grich Offline OP
Member
OP Offline
Member
Joined: Aug 2012
Posts: 71
One of the brands of prefab concrete buildings used by cell companies.

A 6AWG wire through the wall to an existing (and unused) 2AWG ground cable that runs to the other end of the building and ties to the main ground bar.

hbiss #618681 04/09/18 02:09 PM
Joined: Dec 2007
Posts: 6,799
Likes: 18
Retired Admin
*****
Offline
Retired Admin
*****
Joined: Dec 2007
Posts: 6,799
Likes: 18
Originally Posted by hbiss
What's a thermobond building? -Hal
It is a company [Thermo Bond] they makes small out buildings and outdoor cabinets such as you see for smaller Data Centers, Cell Tower equipment storage, et cetera. They can be made out of wood, metal, concrete... If you saw one you'd say "Oh, one of those".


Dean
Photographs:
https://www.instagram.com/deanwilsoncanby/
https://fstoppers.com/profile/deanwilsoncanby
https://www.facebook.com/Dean-Wilson-Photography-112841337020414

Please don't confuse your "Internet Search" with my licenses, certifications and over 30 years experience.

"Thank you for calling Technical Support. If you feel you have reached this number in error, please hang up and press redial."
grich #618693 04/10/18 12:16 AM
Joined: Jan 2009
Posts: 849
Likes: 1
Member
Offline
Member
Joined: Jan 2009
Posts: 849
Likes: 1
I assume you are talking about a copper fed service, and not fiber? Around here, almost every tower company we've worked with only wants fiber and they state that no metallic components of our cable are to enter the building. We end up pulling a di-electric fiber drop and pull a tracer wire with it and leave the tracer outside of the building.

grich #618694 04/10/18 12:50 AM
Joined: Feb 2005
Posts: 12,342
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,342
Likes: 3
Oh yeah, one of those!

I would say you did OK with the ground, though I have to echo what @ffej010 said. I'm surprised that they did this with copper.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
grich #618698 04/10/18 10:37 AM
Joined: Aug 2012
Posts: 71
grich Offline OP
Member
OP Offline
Member
Joined: Aug 2012
Posts: 71
I was, also, since in downtown office building rehabs, CL is pulling out the copper and installing fiber. This tower site is owned by the radio station, so they didn't have a problem with copper coming in.

CL did run fiber and sprinkle the roadsides with new SLICs a year or so ago, presumably preparing for the conversion of this part of the county from farmland to urban sprawl, which is well in progress a mile north of the tower. frown


Moderated by  Silversam 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,262
Posts638,693
Members49,757
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,098 Shoretel
187,703 CTX100 install
186,793 1a2 system
Newest Members
BPopilek, Rich F, LewisR, TDKs79, Buttinset
49,757 Registered Users
Top Posters(30 Days)
dexman 18
Toner 14
TDKs79 8
Who's Online Now
2 members (Curlycord, dexman), 54 guests, and 245 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5