I have a customer with a NEC SV9100 (School) with 100 Pair outside cable between two building with lightning protection on both ends its been there probably from the beginning They are both grounded looks like the same modules on each end 489BCB1-100 Comcode 107895112 Lucent Technologies
There has been (2) separate incidents (1) this year which blew out (2) digital station cards and (1) last year that blew out (1) digital station card
They also had some data equipment that got hit as well (Last Year)
I notice that the NEC cabinets are not grounded so I was going to do that I just wondering if the right lightning protection is installed since its been their for a while
|
|
|
|
Joined: Mar 2018
Posts: 345 Likes: 1
Member
|
Member
Joined: Mar 2018
Posts: 345 Likes: 1 |
Just to make sure, the cards that were blown out had stations on the feed cable?
The Cloud is just someone else's computer!
|
|
|
|
Joined: May 2007
Posts: 5,050 Likes: 3
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,050 Likes: 3 |
What kind of protectors - Carbon or Gas?
If they're gas they S H O U L D protect digital equipment. If they're carbon, they're only good for analog.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Sep 2018
Posts: 68
Member
|
Member
Joined: Sep 2018
Posts: 68 |
This. Get an electrician to test the grounds with a megger. They need to be less than 25 ohms to ground for those protectors to work. I would expect No. 6 or better wire for a 100 pair cable What color are the protectors? There should be black, red or blue things plugged into the lucent terminals you listed, and a big fat ground wire coming out of htem.
|
|
|