Hi Guys,
I'm looking for some relay ideas.
What I would like to accomplish to use my dial selective intercom unit to turn on and turn off items when you dial a ext number to turn on something or off.
For an example, dial ext 2 to turn on a external bell for the garage and have it stay on until you dial the same ext or a different one to turn it off. This would be replacing a TKM-6 Adjunct Switch that has the ringing pairs.
Another idea I would like to play around with is using a relay to turn on or off a closet light or back yard light.
My dial selective intercom unit uses 10 V AC so I really do not have any idea what type of relays I should use to accomplish this.
Also would the relay have to have a constant-power supply for them to operate?
Thanks Brian
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
Brian -
There are latching relays - that lock in to one state or the other until energized again. All the things you're looking to accomplish are do-able.
It may be easier to reverse the power on your DICM. Have the buzzers rest on 10VAC and then switch ground through the ICM. This way (if you have all the grounds in the Power supply commoned) then you can use relay that has a 24VDC coil (using B Battery off your Power Supply).
Sam
"Where are we going and why are we in this hand basket?"
|
1 member likes this:
EV607797 |
|
|
|
Joined: Dec 2002
Posts: 9,423 Likes: 1
Member
|
Member
Joined: Dec 2002
Posts: 9,423 Likes: 1 |
latching relay would do it. I am messing with one now...we use them a lot for access control.
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: Apr 2018
Posts: 151
Member
|
OP
Member
Joined: Apr 2018
Posts: 151 |
Hey Sam and Jeff. I found this item Model: LARY-AC LARY-AC AC Latching Relay with DPDT contacts And here is the website http://www.azatrax.com/latching-relay.html Would something like this work? Now I know this relay can not be used to switch a high voltage item such as a 75 watt light bulb
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
It seems like it would, If you needed to switch higher voltages use that relay to control a relay that had a more "serious" coil. If I remember correctly, this is called a "Class 3" circuit in the electrical business (High Voltage circuit controlled by a low voltage circuit). You should be able to find them in any electrical Supply House (or on line).
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Dec 2002
Posts: 9,423 Likes: 1
Member
|
Member
Joined: Dec 2002
Posts: 9,423 Likes: 1 |
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: Apr 2018
Posts: 151
Member
|
OP
Member
Joined: Apr 2018
Posts: 151 |
Hi Sam,
I need some calefaction on" buzzers rest on 10VAC" what do you mean?
Also when I do reverse wire the power on the DICM, would I reverse both A and B battery?.
Would I leave the 10 VAC for the audible supply or would I need to make any changes to the audible supply and to the audible supply Ground.
One idea that I was thinking about is to get a spare DICM unit and reverse wire it and only use this unit for the relays. And then have a relay to transfer the Tip/Ring pair to the spare DICM unit and when you done making a section for a relay dial the ext for the return relay to transfer you back to the normal DICM unit.
Thanks Brian
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
NO!
A & B Battery stay as they are.
Signal ground becomes 10VAC.
Signal Battery is Ground.
In the new normal condition 10VAC is always present on one side of the buzzer. When you dial a digit, the DICM sends ground.
This is much easier. That Ground now can buzz a buzzer, trip a relay, do whatever...
Sorry for taking so long. I've been offline for a few days.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Apr 2018
Posts: 151
Member
|
OP
Member
Joined: Apr 2018
Posts: 151 |
Thanks Sam,
If I need to use 24VDC to switch a relay, would use 24VDC B Battery Ground as the audible supply and then B Battery as audible supply ground?
What I was thinking since I think I might a have a Expansion Module for my DICM unit is leave the first unit in the original configuration and then use the Expansion Module for switching the relays since the Expansion Module does have a separate audible supply input.
|
|
|
|
Joined: Jan 2005
Posts: 15,378 Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,378 Likes: 13 |
"It may be easier to reverse the power on your DICM. Have the buzzers rest on 10VAC and then switch ground through the ICM. This way (if you have all the grounds in the Power supply commoned) then you can use relay that has a 24VDC coil (using B Battery off your Power Supply)."
Sam Brilliant suggestion, Sam!
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Jan 2005
Posts: 15,378 Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,378 Likes: 13 |
12 volt automotive type relays are dirt cheap and great for these applications. I did something similar in my own home. For example, one code opened one garage door and another code opened the other. Yet another code would override the sprinkler system's timed settings.
I used a 36 station intercom where '3' would open the one garage door '4' would open the other. Because garage doors just needed a momentary contact closure, a regular relay contact associated with each code was all that was needed. For other devices that needed to stay activated, I used a pair of SPDT relays per code, one to perform the switching of the device and the other to latch on the power to that relay. For example, the code for the sprinklers was '5' and when dialed, it would send power to both relays. Through NO contacts on the second relay, power was applied to the controlling relay constantly upon activation. '25' would fire another relay that dropped power to the 'ON' relay pair.
1A2 lamp power supplies are fairly common to provide 10 volts AC. I just sent this output to a 2 amp full wave bridge to convert it to 10 volts DC, which was ample to activate a 12VDC automotive relay. Relays and diodes can turn 1A2 intercoms into magic boxes in no time.
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
You could use your expansion module, but I don't really see the need. As far as what ground to us - ALL your grounds should be commoned (tied together) at the power supply.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
Thanks, ED! That means a lot - especially coming from you!
It was something I thought of when I had to have the DICM flush the toilet in a private bathroom in the Empire State Building. It was a joke that the CEO had. His friends would come out of the bathroom and he would say: "Did you flush?" and then hit the code on the phone. The toilet would flush and he would roar like a lunatic at their expression.
I worked with a plumber who installed a relay operated pump to flush the toilet. I think the guy spent more for that setup than for the whole phone system!
Sam
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
"Relays and diodes can turn 1A2 intercoms into magic boxes in no time."
Amen to that!
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Dec 2002
Posts: 9,423 Likes: 1
Member
|
Member
Joined: Dec 2002
Posts: 9,423 Likes: 1 |
Sam, you gotta tell us how it worked!
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: Dec 2007
Posts: 6,799 Likes: 18
Retired Admin
|
Retired Admin
Joined: Dec 2007
Posts: 6,799 Likes: 18 |
I worked with a plumber who installed a relay operated pump to flush the toilet. Did a bit of "Normally Open" and "Normally Closed" relays in FACP's, but tampers to water mains were the closest I got to something like that. One thing a LOT of women would like is a relay for the toilet seat: Normally Up/Normally Down.
|
|
|
|
Joined: May 2007
Posts: 5,058 Likes: 5
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,058 Likes: 5 |
Jeff, I was struggling with the phone. It was an ITT K20 Wall that had to be modified for some reason. I'm thinking it was a rotary system and ITT didn't make a K-20in a wall model, so I had to take a K10, add a key strip and convert it to tone dial and put in a Tone to pulse converter (because then the numbers would be on the dial and not on the faceplate (where they'd be upside down)...
Anyway the bathroom was tiny - a sink and a bowl. And a phone and it was a pain in the butt. The CEO (who's office it was was breaking my chops about "couldn't I get the job done?" And I said -
"We can make the phone flush the toilet if you want it to!"
And he said - "Really?"
So we got a plumber in. I sent the plumber a 1 second burst of ground which tripped his relay that flushed the toilet and the CEO was happy.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Apr 2018
Posts: 151
Member
|
OP
Member
Joined: Apr 2018
Posts: 151 |
Thank you so much every one for the help. It would have been so cool to see a intercom to flush the toilet.........
Few quick questions. ...
To my understanding the Altronix RB1224 relay will act like a momentary switch. In my application it could be a way to open or close a garage door.
The Altronix RBR1224 relay is a latching relay and stays latched when power is removed. For my application I would like to do the following things. 1. Be able to turn off/on background music in any particular room. 2. Be able to turn off/on a loud bell in the garage and so on. 3. Be able to turn off/on a light.
My power supply is a WECO SD-81824-01 so it looks like the grounds are not commoned (tied together) unless it’s internal, each gourd has its own terminal. I am thinking that I would take the power ether from a extra lug from the block if one is available or just take a extra jumper cable and tie it to the 24vdc from the power supply terminals.
One last question...... Since I will be using few relays, what do you guys recommend for a neat cable management for the 24VDC power.
Here is what I am thinking….. Make a jumper cable from the power supply and connect it to a 66 block. And on the 66 block ether wire the positive and negative like you would tip and ring or do top half of the block positive and bottom half negative.
Please share your ideas.
|
|
|
|
Joined: Feb 2014
Posts: 657
Moderator-1A2
|
Moderator-1A2
Joined: Feb 2014
Posts: 657 |
To my understanding the Altronix RB1224 relay will act like a momentary switch. In my application it could be a way to open or close a garage door. I have a relay wired to a non-locking key on a 2852 (10 button cuckoo clock phone) that opens and closes one of my garage doors. I also use the contact closure adjunct on my partner acs system to do the same thing, but since it has two sets of contacts I can control both doors. Using some voip bits and some creative engineering, I'm able to dial up my garage doors from anywhere and open and close them. The process is deliberately over-complicated to prevent misuse. I have it on a speed dial on my cell phone with pauses added but its dial a number, get second dial tone, dial another number, wait a few seconds and dial a code. When it comes to 1A2 and relays.... Your imagination is pretty much the only limit. Someday I'll dig out my 18 station DICM add-on and use that for relay control for all kinds of things.
|
|
|