Originally posted by ev607797:
Yeah, but HJB, that's jacketed cross connect wire. It's not rated for general wiring use except in very limited applications. It carries the same ratings as patch cord wiring material. It's not rated for riser OR plenum use, so it's not [b]really inside wiring cable. [/b]
I know it isn't "horizontal cable." I was just trying to be funny
You are correct that it is not suitable for horizontal "inside wiring," but not necessarily for the reasons that you mentioned.
There are several different ratings for cable:
CM = Communications
CMR = Communications RISER
CMP = Communications PLENUM
A CM rated cable is just fine for running inside a building as long as it is not running through a plenum or through a riser shaft. Both RISER and PLENUM are specific applications. RISER does not simply mean "non-plenum."
For instance, Systimax's main CAT-5E non-plenum cable (known as "1061") is generally purchased as standard CM cable (1061
C).
The CMR version of the 1061 cable is known as 1061
B, but it isn't purchased all that often because horizontal cable doesn't usually pass through riser shafts.
So, CM cable is fine for "inside wiring" as long as it doesn't need to be UL910 (plenum) or UL1666 (riser) rated.
Hans