HI! There, i have site in Canada i am doing and most of the Data /Tel is ft6 , but there are about 10 or more dual drops that go in pvc in concrete floor but they rise up to second floor to the I.T closet, my question is Can i use Ft4 in this situation and is there a limit of exposed ft4 allowed ?? Thanks :shrug:
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Sep 2010
Posts: 41
Member
|
Member
Joined: Sep 2010
Posts: 41 |
FT4 is fine so long as it is not exposed within a plenum space. It sounds like you're talking about a riser shaft rather than a plenum, so you should be OK. It's only when you're in an air-handling space (dropped ceiling, raised floor, ductwork) that you need to go FT6.
I you are entering a plenum space with FT4, it needs to be entirely enclosed in appropriately-rated conduit. There's no exception for just a few inches.