I've already connected a 50 pair wire btw two buildings and on either end have two PortaSystems Gas filled punch down blocks. The wire is outdoor rated and I also put Plastic conduit around it for added protection. It's buried over 2' in the ground and I have the metal sheath grounded to 3 lightning rods on both buildings. I am still getting "spikes" from lightning cause it is taking out my Merlin Legend MLX-16DP phones at about 3/storm. I would have thought those expensive PortaSystem punch down blocks would take care of it but I am a novice and I guess I need additional lightning protection. Please Help and try to use whole words because I am not in this field and don't know all that shorthand "jargon" on the other posts. Thanks for the help!

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
First question I have, is the phone system grounded to the same source as the cable sheath? If that answer is yes, take a volt meter and read from the power ground (you can use the ground of a grounded outlet) to your system ground, you should read near zero ohms, not more than 5 ohms. If this is also true, what voltage are your porta systems protectors? If they are the high voltage and the only thing on them are the phones use a low voltage protector. Don't use low voltage on the CO lines or anything other than your low voltage digital phones. Hope this helps


Retired phone dude
Joined: Feb 2005
Posts: 1,037
Member
Offline
Member
Joined: Feb 2005
Posts: 1,037
Is it taking out the phones only, not the ports too? Are these phones only out across this feeder? If they are and the system/ports aren't getting hit then I would check the bonding/grounding at the far end.
Justbill is ...so very correct! How many times I've had to explain to a customer who purchased Porta equipment, or the like, and didn't purchase the low-voltage modules.
Lightning is very fast,very dangerous, and always unforgiving.

Joined: Feb 2005
Posts: 12,344
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,344
Likes: 3
I am a novice and I guess I need additional lightning protection. Please Help and try to use whole words because I am not in this field and don't know all that shorthand "jargon" on the other posts.

Best whole words I can give you is to hire someone who IS in the "field". If this were easy to do and all you needed was available on the internet you wouldn't be having a lightning problem.

Each case is different and we can't see what you have, what you have done and how you did it. All three are vital and without actually being there to evaluate there is no way anybody here can give you any advice that would be meaningful.

This is costing you money. Stop wasting it by thinking that this is a do-it-yourself project.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
Hal has a very good point.


Retired phone dude
Joined: May 2003
Posts: 2,267
Member
Offline
Member
Joined: May 2003
Posts: 2,267
This started in the Avaya Forum, moved to equipment repair (he has a few smoked phones), then I suggested that he come here.
It is only the phones at the remote location getting taken out, not the ports. I should have realized that it had to be on the remote end grounding/lightning protection.
In my defense, I can only offer that we specialize in fixing the phones once the lightning has hit and do not install them.

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
I'm betting he has a difference in potential from his equipment ground to the sheath ground. The low voltage protectors should help, but as Hal says find the cause first.


Retired phone dude
Joined: Dec 2005
Posts: 7
Member
OP Offline
Member
Joined: Dec 2005
Posts: 7
Nothing like getting a rear end chewing from Hal.
The porta sytems protector is a model 581 P2. The sales representative at GrayBar said this would be sufficient for my phones and phone system. Yes only the phones are getting smoked not the ports. The ohm reading was 0.0.

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
If all grounds are equal to the power neutral than the only thing it can be is inductive to the cable pairs in between the buildings. Use the low voltage protectors on the digital phones and ground any unused pairs in the cable. What you are describing is a difference in ground potential, but your ohm reading says you don't have one. The 581 P2 is the whole terminal without the protectors, the 581 series has 250v 75v and 350v modules, you'd want the 75. Again you just want these for the digital phones, nothing else. One more thing, even though you're not indicating a difference in potential, it's sure acting like one so make sure all grounds are bonded together, I'd about bet they are not. Also you say "3 lightning rods" Do you mean ground rods that the building lightning protection is grounded to?


Retired phone dude
Joined: Aug 2005
Posts: 6,692
Member
Offline
Member
Joined: Aug 2005
Posts: 6,692
You said you connected the two buildings. My question would be, was this system up and running PRIOR to connecting the two buildings? Where I'm going with this is, perhaps the spike has nothing to do with the underground construction. You may have the front door bolted, but left the upstairs window open.

Joined: Sep 2005
Posts: 472
Member
Offline
Member
Joined: Sep 2005
Posts: 472
Panamax/Towermax makes IROBs (In Range Out of Building)surge protectors specifically for the ATT/Lucent/Avaya product line. Those system sets need more protection then your gas tubes can provide.

PS I gotta agree with Hal here. Why does everbody think what we do is some darn easy - do it yourself until they do it and it doesn't work!

Joined: Aug 2003
Posts: 5,154
Likes: 2
Moderator-Vertical, Vodavi
*****
Offline
Moderator-Vertical, Vodavi
*****
Joined: Aug 2003
Posts: 5,154
Likes: 2
Quote
Originally posted by towboatusa:
The sales representative at GrayBar said this would be sufficient for my phones and phone system.
I'm just happy if my Graybar rep can find the part number I'm looking for.

Joined: Jan 2005
Posts: 15,381
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,381
Likes: 13
Well, I might as well add my two-cents here. First of all, the 581 series of protectors are not true primary protection devices. The manufacturer claims they are, and I see hundreds of them out there as primary protectors, but they just plain and simply AREN'T. They are fine for secondary protection as is indicated by the way they are constructed.

They don't have a sealed splice chamber or compartment to contain the gel-filled cable. It is improper (and illegal) to punch down a gel-filled cable directly on a block. It must be contained within a UL listed enclosure. That requirement by itself rules out the legitimacy in using the 581's in your situation.

What needs to be installed is a TRUE building entrance terminal, one made by TII, Emerson Network Power or even Porta Systems. These need to be equipped with gas or solid-state protector modules. The entrance terminal must be grounded to the same exact point that the building's electrical service is grounded. This must be done using a #6 copper conductor minimum. Three ground rods, especially if they are not bonded together (and to the electrical service, water/gas piping and building frame) are plain and simply asking for problems.

Then, a reasonable distance of inside wiring (I prefer to provide a bit of separation, at least 25 feet) needs to be run from the primary protection in the building entrance terminal to the secondary protector, A.K.A. the Porta Systems 581 block. Once this block is equipped with 75 volt protector modules, you will have a truly protected underground cable installation.

If you do have a 50 pair gel-filled cable that is punched-down directly on 581 units, you do not have a professional installer. The original installer does not know what they are doing. It has already been mentioned here that this work isn't as simple as it seems. That is why we are here to assist.

I suggest that you contact a professional telephone/CATV cable contractor (there's a separate listing in the Yellow Pages for this). If you can't find one, try to see who your local phone company is using as a sub contractor for outside cable installation. The phone company won't tell you who it is; you will just need to keep an eye out for a truck with someone working on a pole that is not the local power, cable or telephone cable company. If all else fails, try to locate a local Henkels & McCoy office. They do this stuff nationwide for telephone companies and they seem to know what they are doing.

You really do seem to be losing a lot of money because of an unprofessionally-installed protection system. It will probably cost over a thousand dollars to do it right, but it seems to be adding up for your business already. Maybe it's time to finally get it done right.

I sure hope that you take this as guidance and not criticism. Lots of companies out there can install phone systems and make them work well, but when outside cable is involved, the whole playing field changes.


Ed Vaughn, MBSWWYPBX
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
As usual Ed you've added something I didn't even think about and that's the proper closure for this set up. I was concentrating on the bonding only. Even if he doesn't have the proper entrance terminal for the cable, if everything is properly bonded and rated he shouldn't be having the trouble he is, at least in my opinion. He is getting a foreign voltage on the pairs that feed the phones and just from the description of what is happening it sounds to me like the grounds are not equal. I knew we could count on you to set us straight.


Retired phone dude
Joined: Sep 2004
Posts: 1,436
Member
Offline
Member
Joined: Sep 2004
Posts: 1,436
Gee, if words were money we'd all be broke if that was Ed's two cents worth.


Joe
---
No trees were harmed as a result of this posting; however, many electrons were severely inconvenienced.
Joined: Jan 2005
Posts: 15,381
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,381
Likes: 13
Git back on the porch, Uncle Lonnie! Doesn't your court order restrict you from associating with other convicted felons?

OK, that was tacky, but hey, I had to change my avatar since you stole mine and I needed an identity.


Ed Vaughn, MBSWWYPBX
Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Offline
Member
Joined: Dec 2004
Posts: 5,722
Okay, girls, let's ply nice ! smile

Since Ed used up two cents, leaving me only a red cent ($.001) here it is.

All the above PLUS make sure the cathatic protection and lightning grounding system have the same potiental. Depending on the situation the cathatic tied to red iron can go "high" and cause issues.

Just a thought. wink

KLD.


Ken
---------
Joined: May 2004
Posts: 187
Member
Offline
Member
Joined: May 2004
Posts: 187
I have seen installs put both the outside cable and the inside cable on the same side of the block. They thinks it looks nice... But this unit has a in and out side to it so that the protector works properly. I would make sure that the unit is installed correctly...

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
Another good point. I assumed it was wired in correctly.


Retired phone dude
Joined: Jun 2004
Posts: 100
Member
Offline
Member
Joined: Jun 2004
Posts: 100
Try using IROB'S on both ends

Page 1 of 2 1 2

Moderated by  EV607797 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,306
Posts638,894
Members49,771
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,987 Shoretel
190,166 CTX100 install
188,348 1a2 system
Newest Members
Mansour, Dave Simmons, Soulece, Robbks, A2A Networks
49,770 Registered Users
Top Posters(30 Days)
Toner 17
teleco 6
dexman 6
dans 5
jsaad 5
Who's Online Now
1 members (mongo5150), 120 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5