Originally posted by fuzzyone45:
...The same power supply was also being used to power a door control system and they saw no power interuptions.
Which power supply are you refering to?
1. The ACS's power supply as it affects the operation of a door adjunct
2. A UPS/Conditioner that is outputing power to both the system and the door control
3. The specific power circuit in the facility that provides power to both the system and the door.
At first glance (and assuming that both systems were OK to begin with), it seems to me that you may have an undervoltage situation that goes beyond the tolerances of the Partner, "frying" the translation without replacement, which causes the system to default to the factory translation.
If my thinking is correct, and since it looks like the brownouts are happening at more or less regular intervals, I'd check to see what else kicks in to draw juice from the circuit.
Perry