CL3 is 300v insulation, CL2 is 150v. This is prohibited from being marked on the cable or reel per the NEC. You are not supposed to make the judgement as to what to use, rather you are supposed to look at the label listing on the power source which will tell you what wiring method to use- Class 1, CL3 or CL2.