I am pretty sure that he meant that a cloud covering the sun meant the possibility of a thunderstorm. I think it was more of an exaggeration of strange weather that can happen.

Bonding building grounds together is why they make shielded cable. To isolate the cable pairs from differences in ground potential.

Throwing a cable in the ground or in the air and punching it down on a Panamax "protector" isn't how it's done. People actually believe that this is all that needs to be done, but they are wrong, way wrong.


Ed Vaughn, MBSWWYPBX
Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#10546 03/29/06 02:11 PM
Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Offline
Member
Joined: Dec 2004
Posts: 5,722
Amen, Brother EV, you are preaching the word on grounding and bonding. Ground the world round is only as good as the bond.

Okay, now pass the collection plate. :thumb:

KLD -- The one-eyed.... wink


Ken
---------
#10547 03/29/06 03:20 PM
Joined: Sep 2005
Posts: 2,049
Member
Offline
Member
Joined: Sep 2005
Posts: 2,049
Agree

Ground Is Ground The World Around And James Is Not The Only Bond That Protects And Serves ! wink


Let It Be , I live in a Yellow Submarine . SCCE
#10548 03/29/06 03:27 PM
Joined: Mar 2006
Posts: 175
Member
Offline
Member
Joined: Mar 2006
Posts: 175
Yes it was an exaggeration. But electrical storms almost always caused problems. The earth's resistivity was so high that the current flowing through the ground found its way through the bulding to building conductors and zapping anything in its way. Even proper sheath bonding didn't help. I thought that beefing up the grounds at each building would help but it did not. In fact I probably made things worse. Once a common ground was installed the problem was no more.

#10549 03/29/06 04:40 PM
Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
I would have to disagree that the original bonding was proper because a 25+ pair cable sheath is the approximate electrical equivalent of a #6AWG conductor. If all bond clamps and attachments were the correct type and installed properly, there would have been no need to bond the buildings together. Doing that is not always the best thing to do in the event of an electrical fault, especially if there are separate electric services.

I am glad to hear that all worked out though. I am a former electrician so I am bit biased about doing things to code, and then I am also a Pr&^k about Bell System standards. Both take this subject very seriously and specifically address grounding and bonding as priority #1.

Check out the "Outside Wire Construction" category if you are interested in more discussion on this topic.

This is a subject that will be strongly debated until we don't have lightning anymore. If that happens, I guess we won't be here either!


Ed Vaughn, MBSWWYPBX
#10550 03/29/06 05:22 PM
Joined: Sep 2005
Posts: 2,049
Member
Offline
Member
Joined: Sep 2005
Posts: 2,049
Lightning according to NASA

Dec. 5, 2001: Lightning. It avoids the ocean, but likes Florida. It's attracted to the Himalayas and even more so to central Africa. And lightning almost never strikes the north or south poles.

These are just a few of the things NASA scientists have learned using satellites to monitor worldwide lightning . So if I where the obhhbe I would say drive your ground rods into the North Pole . My humble personal opinion . :thumb:

Just kidding ! smile


Let It Be , I live in a Yellow Submarine . SCCE
#10551 03/30/06 04:46 AM
Joined: Mar 2006
Posts: 175
Member
Offline
Member
Joined: Mar 2006
Posts: 175
The common ground is laid in a trench between all buildings. It is aprox 1" diameter of stranded copper and put in a bed of condacrete. It is about 350 feet long. From the ground cable, spurs go to each building and are a little smaller in diameter. They terminate in a copper plate 1/4 " thick and 12" X 3". From the copper plate, #2 AWG. goes to the equipment room and is terminated to all equipment. Also the electrical service in each building, there are only three, are bonded to this ground system. A company from Canada, was subbed to do the gob. They specialize in cell tower and antenna grounds as well as communications buildings when unusual situations are encountered. After they put this in, everything ran perfect. It has been four years.

#10552 03/30/06 04:52 AM
Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
Wow. That's some serious grounding and bonding. It must have been expensive!


Ed Vaughn, MBSWWYPBX
#10553 03/30/06 07:37 AM
Joined: Oct 2004
Posts: 812
Member
Offline
Member
Joined: Oct 2004
Posts: 812
I used to work for an elecrical contractor. We would install exspensive grounding grids for cell towers.

Different soils also effect the ground potential. Sandy dry soil is a terrible ground. Hardpack clay would be most ideal. I guess in florida if you drive the rod deep enough you would hit water and you would have a great ground. Hey, Is ligtning an AC or DC crkt. or is it both?

#10554 03/30/06 10:08 AM
Joined: Mar 2006
Posts: 175
Member
Offline
Member
Joined: Mar 2006
Posts: 175
Yes, It was very expensive. All expenses had to be paid for the initial visit and the installation visit for 2 techs. They contracted local help to do the digging but the techs did the connections. All nodes and splices were blast welded together.
Soil types made a difference. They took several samples. They also took 3 sets of earth resistivity data and used the average for the design.

Page 3 of 3 1 2 3

Moderated by  MooreTel 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,290
Posts638,801
Members49,767
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,358 Shoretel
189,028 CTX100 install
187,401 1a2 system
Newest Members
Robbks, A2A Networks, James D., Nadisale, andreww
49,767 Registered Users
Top Posters(30 Days)
Toner 22
teleco 6
dexman 5
jsaad 3
dans 3
Who's Online Now
1 members (dexman), 132 guests, and 406 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5