#447823 02/05/08 12:40 PM
Joined: Nov 2001
Posts: 1,640
Moderator-NEC
*****
Moderator-NEC
*****
Joined: Nov 2001
Posts: 1,640
MacOSX

I was not pointing my comment at you. I was pointing the comment at ERICO.
It would seem that it would make an install not pass an inspection. Especially if the Inspector pays attention to the last sentence

"300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies,
boxes, cabinets, and fittings shall be securely fastened
in place. Support wires that do not provide secure
support shall not be permitted as the sole support.
Support wires and associated fittings that provide
secure support and that are installed in addition to the
ceiling grid support wires shall be permitted as the sole
support. Where independent support wires are used,
they shall be secured at both ends. Cables and raceways
shall not be supported by ceiling grids.


It is a very Grey area because apparently it is not really clear in Section 800.

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#447824 02/05/08 01:15 PM
Joined: Dec 2007
Posts: 2,033
Moderator-Toshiba
Moderator-Toshiba
Joined: Dec 2007
Posts: 2,033
Quote
Originally posted by ttech:
MacOSX

I was not pointing my comment at you. I was pointing the comment at [b]ERICO
.
It would seem that it would make an install not pass an inspection. Especially if the Inspector pays attention to the last sentence

"300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies,
boxes, cabinets, and fittings shall be securely fastened
in place. Support wires that do not provide secure
support shall not be permitted as the sole support.
Support wires and associated fittings that provide
secure support and that are installed in addition to the
ceiling grid support wires shall be permitted as the sole
support. Where independent support wires are used,
they shall be secured at both ends. Cables and raceways
shall not be supported by ceiling grids.


It is a very Grey area because apparently it is not really clear in Section 800. [/b]
No problem, I didn't take it as such. :toast:

I was agreeing completely, but pointing to the web-site, incase you didn't think it was an actual Eric/CADDY product.

You are right on about the inspection/inspector, for sure.
That would, or at least shouldn't ever fly!


- Tony
Ohio Data LLC
Phone systems, data networks, firewalls and servers in Central Ohio.
Some people aren't used to an environment where excellence is expected.
Page 2 of 2 1 2

Moderated by  Silversam 

Link Copied to Clipboard
Newest Topics
Admin Program for XTS Systems
by EV607797 - 07/11/25 10:22 AM
Compatibility with Verizon FIOS phone lines
by ringtone - 07/10/25 03:23 PM
Tone / Probe repair
by jsaad - 07/02/25 03:49 PM
Forum Statistics
Forums84
Topics94,564
Posts640,172
Members49,868
Most Online5,661
May 23rd, 2018
Newest Members
FranzBos, Chuck Lowe, Ma Bell Brat, Shadowchan454, SuperDave99
49,868 Registered Users
Top Posters(30 Days)
Toner 12
R4+Z 3
C5Z 3
Who's Online Now
0 members (), 10 guests, and 89 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998 - 2025
Powered by UBB.threads™ PHP Forum Software 8.0.0