OK, I know I'm opening up a can of worms here (I don't know if I should continue this in my previous post or start anew)
In my earlier post "gen. quest." I discussed how "I" terminated outside plant cables(burial/arial)and how I find grounds. Several replies said I was doing my grounds wrong. I did a "search" on grounding on came up with numerous post,some which frightened me and others that basically did the same as me.What is wrong with "Meter to AC volts, one leg of meter plug into right side of outlet, other leg touching metal water pipe or building beam, and if I read 120V I know that it is grounded" To me, this is an electrical ground.Why should I create a differnt ground with a better potential to ground? A lightning strike is always looking for least resistance to ground. By using my stated method am I not creating a path THRU my equip. yet if I create another ground (grounding rod) with less potential isn't that going to attarct the strike more (and hence THRU my equip)?

One other thing, gotten into arguments with others concerning path of ground wire. I have always done straight as possible, short as possible.Several co-workers, when grounding a data rack, would put a curley ( several wraps around a screwdriver handle)tail before attaching to rack and ground.

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#473689 09/15/05 03:20 AM
Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
First, to address your question about the "wrapping a ground wire around a screwdriver handle" thing, I can't imagine that an extra foot or two of wire would really make much of a difference. Now that I think about it, that might actually protect the ground connection from being pulled loose if the rack moves slightly. So on that note, I kind of like that idea. Still, my preference would be to use #6 for that type of grounding; something that's a little tough to wrap into a tight coil.

Grounding conductors should always be connected to the nearest building grounding electrode, being a metallic water pipe, rod or metal building frame member. It's also important that all of these be bonded together. I have seen way too many instances, for example where an underground telephone cable terminates in an outdoor pedestal, being grounded to a separately-installed ground rod. This is where things can get dangerous because of the difference in ground potential. I have taken voltage readings between a local building ground and these separate rods that have been well into the double digits!

Always remember that all metal, whether it be pipes, racks, conduits or building steel must always be bonded together. Make it a practice to use #6 copper for your protector ground conductor and you will be all set.

------------------
Ed
---------
How come there's always enough time to go back and fix it a second time?


Ed Vaughn, MBSWWYPBX
#473690 09/15/05 04:16 AM
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
Pretty much what Ed said. It's the difference in potential that will kill ya. As far as searching for a ground from the hot side of AC, like I said in your other post you'll find ground, but not necessarily a GOOD ground. Wrapping the ground around a screw driver?? For one if you can do that you're not using a large enough gauge for your ground. We did and I still do use a small gauge wire and wrap it around a screw driver like when connecting aerial drop to a paging speaker. This makes a fuse so if the drop gets hit by lightning the make-shift fuse will blow. Lightning likes to go in a straight line so by putting the wraps in it causes your fuse to blow out instead of the speaker. Believe it or not this works quite well.


Retired phone dude
#473691 09/15/05 10:00 AM
Joined: Apr 2005
Posts: 69
Member
OP Offline
Member
Joined: Apr 2005
Posts: 69
So, If I take a piece of ground wire (I use #10 and/or #12 mostly)about a foot in length and put several coil type loops (almost like a spring)that will act like a fuse? Wouldn't the lightning strike "jump"?

#473692 09/15/05 10:29 AM
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
I've never tried it with larger gauges, but I'd say the theory is the same. The old 22 gauge IW would blow at the corners if it had a direct lightning strike ( I have personally seen where it blew a hole through a wall into the next room). Personally I don't put 90 degree bends in my ground.


Retired phone dude
#473693 09/15/05 03:02 PM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
When you coil a wire around that screwdriver you are making an "inductor". An inductor will actually resist changes in the amount of electric current passing through it. If the current starts to increase, the inductor will generate a voltage that tends to oppose the change. Not a good idea for a ground, right? A few large loops near the ground bolt acting as a stress relief like Ed suggests is a good idea. Numerous tightly wound coils is not a good idea. Tight bends like "justbill" suggests to avoid, is also a good idea.

#473694 09/15/05 04:27 PM
Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
Wow, Twisted, you paid a lot more attention in science class than I did. I was thinking more of a stress relief solution for bonding connections. I figured just a foot or so of wire shouldn't make a big difference in a coil.

By the way, any word from your friend on the RCA Guide Plus issue?

------------------
Ed
---------
How come there's always enough time to go back and fix it a second time?


Ed Vaughn, MBSWWYPBX
#473695 09/16/05 12:19 AM
Joined: Jul 2005
Posts: 1,184
Member
Offline
Member
Joined: Jul 2005
Posts: 1,184
Ed,

After that last post, I asked him again and he was going to check something for me. He then left on vacation. I'll let you know when he's back.


Moderated by  EV607797 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,290
Posts638,801
Members49,767
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,372 Shoretel
189,056 CTX100 install
187,410 1a2 system
Newest Members
Robbks, A2A Networks, James D., Nadisale, andreww
49,767 Registered Users
Top Posters(30 Days)
Toner 22
teleco 6
dexman 5
Who's Online Now
1 members (Toner), 100 guests, and 419 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5