The Standards The performance tests and their procedures have been defined in the ANSI/TIA/EIA-568-B.1 standard and the ISO/IEC 11801 standard. The TIA standard defines performance in categories (Cat 3, Cat 5e, Cat 6, Cat 6A) and the ISO defines classes (Class C, D, E, EA, F and FA). These standards define the procedure to certify that an installation meets performance criteria in a given category or class.
The significance of each category or class is the limit values of which the Pass/Fail and frequency ranges are measured: Cat 3 and Class C (no longer used) test and define communication with 16 MHz bandwidth, Cat 5e and Class D with 100 MHz bandwidth, Cat 6 and Class E up to 250 MHz, Cat6A and Class EA up to 500 MHz, Cat7 and Class F up to 600 MHZ and Cat 7A and Class FA with a frequency range through 1000 MHz.
The standards also define that data from each test result must be collected and stored in either print or electronic format for future inspection.
The Tests Test Parameter TIA-568-B ISO 11801:2002 Wiremap Pass/Fail Pass/Fail Propagation Delay Pass/Fail Pass/Fail Delay Skew Pass/Fail Pass/Fail Cable Length Pass/Fail Information only Insertion Loss (IL) Pass/Fail Pass/Fail Return Loss (RL) Pass/Fail (except Cat3) Pass/Fail Near-End Crosstalk (NEXT) Pass/Fail Pass/Fail Power Sum NEXT (PSNEXT) Pass/Fail Pass/Fail Equal-Level Far-End Crosstalk (ELFEXT) Pass/Fail Pass/Fail Power Sum ELFEXT (PSELFEXT) Pass/Fail Pass/Fail Attenuation-to-Crosstalk Ratio (ACR) Information only Pass/Fail (except Class C) Power sum ACR (PSACR) Information only Pass/Fail (except Class C) DC Loop Resistance Pass/Fail
So if any device (including the Net Chaser) performs all the above tests and records them isn't it a certifier? Granted, some testers perform many of the above tests digitally as opposed to using analog frequencies, but isn't that what a network is supposed to do...transport data?
Last edited by Derrick; 01/14/15 10:26 AM.
www.myrandomviews "Old phone guys never die, they just get locked in some closet with an old phone system and forgotten about" Retired, taking photographs and hoping to fly one of my many kites.
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Jun 2005
Posts: 370
Member
|
Member
Joined: Jun 2005
Posts: 370 |
Maybe not my smartest move, but I went with the Ideal Lantek 2 1000Mhz with laser fiber kit. New but was priced close to the refurbished/used Flukes without the fiber kit.
Do the job right the first time.
|
|
|
|
Joined: Jan 2008
Posts: 3,821
Retired Moderator
|
Retired Moderator
Joined: Jan 2008
Posts: 3,821 |
Maybe not my smartest move, but I went with the Ideal Lantek 2 1000Mhz with laser fiber kit. New but was priced close to the refurbished/used Flukes without the fiber kit. Well, the choices are limited, and costly, when you need to have a fiber tester. Looks like you made a good one.
www.myrandomviews "Old phone guys never die, they just get locked in some closet with an old phone system and forgotten about" Retired, taking photographs and hoping to fly one of my many kites.
|
|
|
Forums84
Topics94,512
Posts639,931
Members49,844
|
Most Online5,661 May 23rd, 2018
|
|
1 members (yeloshak),
275
guests, and
47
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
|
|