I had an interesting experience recently as I was sent to extend from the Verizon DMARC to a CISCO router located in a shopping mall a 56 kbps line. Only thing was, I did not know that the pinout configuaration at the DSU/CSU was different from a T1 Pinout (1, 2, 4 and 5) of which I have installed many in my lifetime. So, just in case some one else runs into this, the pinout for a 56/64 kilobit circuit is 1, 2, 7 and 8. Here is also a handy link for reference: https://www.ciscosystems.com/en/US/...4/software/user/guide/boapin.html#wp4769 . I am sure that if it has happened to me, it might just happen to someone else. Just want to pass on a tip to others that might run into this situation in the future.............especially if you are in the Rent - a - Tech business
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
Hey man I was wondering for what reason would I need to put in a crossover cable at a T1 Dmark extension? I have been working on one for a few days and bout pulled my hair out (although I aint got much) but what would be the reason for it not to work even after I punched down all four pair? Can you help me?
I have seen it with some of the ClEC's IAD where you need a T1 crossover cable instead of the standard T1 cable. I think it is the way the port was configured from the carrier. You know for a T1 cable you use pins 1,2 and 4,5 for a straight cable and reverse one end to make a crossover cable.
Zapato, I know this post is from a long time ago, but I have a question if you are still around. Is that 1,2,7,& 8 straight through, or 1,2 to 7,8(and visa versa)? Since it only shows one side I was thinking it was straight through. If it is straight through, wouldn't a standard patch cord work, and the other pairs are just ignored?
The reason for the question is I did in install yesterday, and used a standard patch and it did not work. That is when they told me, use 1,2,7 & 8. I asked were they crossed(1,2 to 7,8) and the engineer acted like he had no idea what I was talking about. Obviously since a cable has two ends. I wanted detail, but I didn't get any.
I ended up using the standard patch cable, cutting off one end. So we have
Conn - 1 1- W/O 2- O/W 7- W/Br 8- Br/W
Conn - 2 1- W/Br 2- Br/W 7- W/O 8- O/W
All the other pins have their normal 568b colors, but since they are not used I am assuming they are ignored.
After I redid the cable and installed as requested, the circuit went from down/down to up/down. I do not know if it is a provider issue or a problem with my cable.
56K circuit is 1,2 - 7,8 straight through. If you setup requires a cross-over then somethings wrong. If with your cross-over it half works, I would try and reterminate the cable.
Hello. I hope this is the right forum. I don't gave much experience with csu/dsu wiring, so please forgive me.
We had a telco provider extend a 56k circuit from the demarc to our computer room. I always thought that there should be two pairs. However, I only have one pair. Is there something I am missing?
This circuit will be going directly into my cisco router (wic).
My wiring was straight through for my question. A standard patch cord would(and did)work fine. The customer insisted I hand make a cable using only 1,2 and 7,8, because they were sure the extra pairs were causing the circuit to fail. I knew that was hoey, but I couldn't prove it to them. At least not until two weeks later when AT&T finally got the circuit provisioned properly...