I just installed a RG-11 cable from one building to another. One side will be connected to the circuit providers Demarc and the other to an MDF closet. The circuit side will be grounded on the Demarc. Do I also need to ground on the MDF side? If so, is there a coupler I can use that has a grounding screw or something to connect to the MDF ground bar? Thanks in advance.

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#474577 12/21/07 02:46 AM
Joined: Dec 2002
Posts: 9,424
Likes: 1
Member
*****
Offline
Member
*****
Joined: Dec 2002
Posts: 9,424
Likes: 1
They will probably just put in a ground block where the coax comes in.


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
#474578 12/21/07 04:02 PM
Joined: Dec 2004
Posts: 1,106
Member
*
Offline
Member
*
Joined: Dec 2004
Posts: 1,106


Trump 2020
Proud 1 star member.
#474579 12/21/07 04:09 PM
Joined: Dec 2002
Posts: 9,424
Likes: 1
Member
*****
Offline
Member
*****
Joined: Dec 2002
Posts: 9,424
Likes: 1
Yes, that is what they normally install, at least around here. I have one where the underground cable comes in and the drop cable to the splitter connects.
However, I am not sure how it is done with an aerial run between buildings. Ed would be your best source of information.


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
#474580 12/21/07 05:58 PM
Joined: Feb 2005
Posts: 12,344
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,344
Likes: 3
By code it's supposed to be grounded with one of those ground blocks where it enters each building. Unfortunately that can cause the coax to carry a part of the electrical neutral current since it is essentially in parallel with the neutral conductor running between the buildings or out in the street.

This may or may not be a problem.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
#474581 12/22/07 09:38 AM
Joined: Jan 2004
Posts: 226
Member
OP Offline
Member
Joined: Jan 2004
Posts: 226
Yea, thats what I was looking to find. Thanks

#474582 12/24/07 04:31 AM
Joined: Jun 2007
Posts: 356
Member
Offline
Member
Joined: Jun 2007
Posts: 356
The "ground potential" refers to how well each buildings ground is grounded.

If building A has a 5 ohm ground and building B is 1 or 2 ohms, your cable may become a ground path for for building A, with current seeking its path of least resistance to ground.

Be very aware of your "ground potential" before grounding BOTH sides of the cable to biuilding ground.


it's all tip and ring
#474583 12/24/07 05:20 AM
Joined: Sep 2006
Posts: 3,290
Member
*****
Offline
Member
*****
Joined: Sep 2006
Posts: 3,290
I have a similar question concerning a house I'm working on. The garage, which has one door opener, one 220V heater, three light switches and some lamp fixtures, is fed from the main house via a buried Romex 12-2 w/GRD. There is no sub-panel, no ground rod, no building bonding point, no nuttin'.

To what do I bond my coax and 6-pair telephone buried wire? Do I create the building ground, by sinking my own ground rod(s)? Does that change the electrician's responsibility to install a ground rod?

It is my interpretation of the NEC that an outbuilding with three or fewer electrical circuits (in this case, one) does not need a sub-panel or a ground rod. So that's what the electrician must have reasoned, too.

Any thoughts?


Arthur P. Bloom
"30 years of faithful service...15 years on hold"

#474584 12/24/07 07:30 AM
Joined: Dec 2002
Posts: 9,424
Likes: 1
Member
*****
Offline
Member
*****
Joined: Dec 2002
Posts: 9,424
Likes: 1
How do you have a 220v outlet running off a 12/2 cable. That is pretty scary.


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
#474585 12/24/07 08:02 AM
Joined: Dec 2005
Posts: 2,928
Member
Offline
Member
Joined: Dec 2005
Posts: 2,928
Jeff you can do it..no neutral is used.


I Swear I did not touch anything bash
Page 1 of 2 1 2

Moderated by  EV607797 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,306
Posts638,894
Members49,771
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,910 Shoretel
190,069 CTX100 install
188,260 1a2 system
Newest Members
Mansour, Dave Simmons, Soulece, Robbks, A2A Networks
49,770 Registered Users
Top Posters(30 Days)
Toner 17
teleco 6
dexman 6
jsaad 5
dans 5
Who's Online Now
0 members (), 71 guests, and 32 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5