We have been having lightning problems at a customer site. The customer wants us to install a new grounding system. I am trying to figure out which protector I need for the extension ports. Below is an example of what I am looking for. I need to know what clamping voltage is required for the ports and
the proper fuse rating.

ITW Linx


Burgie13

www.bdtelecom.net

"Don't believe anything that you hear and only half of what you see"
Nortel Phone System Service
VoIP Demo

Nortel Phone System Service in Canada


Do you need a Nortel Phone System technician or specific Nortel parts?
Atcom to the rescue! Our telephone techs have qualified experience servicing and troubleshooting Nortel CICS, MICS, & BCM telephone systems.
Service in Canada from sea to sea.

Joined: Jun 2005
Posts: 2,256
Member
Offline
Member
Joined: Jun 2005
Posts: 2,256
You can use the 39's, but you will probably be better off using the 75.


Richard
AVAYA-NORTEL-SAMSUNG-PANASONIC-MITEL
www.acceleratedtelecom.com
Joined: May 2007
Posts: 231
Member
Offline
Member
Joined: May 2007
Posts: 231
I have, in the past spoken with nortel about this issue and i believe there are no fuse's made that will protect a norstar set.The set operates at about 25 v dc and was told anything more than operating voltage will blow the set.There was a jack"rj11" that had a built in fuse that was the only thing that was supposed to work "was recomended 1 station side 1 switch side".
Also only time i ever experenced a lightning hit was with off premise phones "3 building site"never blew 75 volt fuse but toasted phones.Also when push came to shove off premise sets were not supported by nortel.

Joined: Apr 2007
Posts: 894
Member
Offline
Member
Joined: Apr 2007
Posts: 894
we had a bunch of multi extension fused protectors at our old site for our 8x24, we had a tie cable that liked getting hit by lightning. if i can get to the old site i will see if there are any left to get you a name, 14 of the 16 buildings over on the campus are gone, so im not too sure


Jay, a recovering IT guy
Joined: May 2010
Posts: 86
Member
Offline
Member
Joined: May 2010
Posts: 86
I have had very good luck with ITW-LINX UP2B-39 on both ends. To check your protection ground, take a loop current reading, then move your clip from the grd. side of the line to the protection grd. it should read 30% or better, less than that tells you have a poor protection grd. Also check all grds. available, The reference should be 3 ohms or less. This checks the Multi- Neutral.


Moderated by  MooreTel 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,290
Posts638,801
Members49,767
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
212,367 Shoretel
189,047 CTX100 install
187,409 1a2 system
Newest Members
Robbks, A2A Networks, James D., Nadisale, andreww
49,767 Registered Users
Top Posters(30 Days)
Toner 22
teleco 6
dexman 5
jsaad 3
dans 3
Who's Online Now
0 members (), 134 guests, and 389 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5