#259676 10/19/05 03:25 AM
Joined: Oct 2005
Posts: 1
Member
Member
Offline
Joined: Oct 2005
Posts: 1
Hi newbie here. I'm ordering new PRI circuits from AT&T. They claim that they no longer extend the circuit to a smart jack in our phone room. The local telco's also decline to do it because it is an AT&T circuit. Our equipment vendor also declines. has anyone ran into this problem and how did you rectify it?
Thanks

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#259677 10/19/05 04:18 AM
Joined: Jan 2005
Posts: 15,402
Likes: 18
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,402
Likes: 18
We do it all the time on our systems and it's really pretty straight-forward. We just run a shielded category 5 cable, put a plug on one end and a jack at the other end. It's really supposed to be a "smart" jack, but a correctly-wired 568A or 568B connection will work just fine.

I have to tell you that if your vendor won't do it, then maybe you need another one. You may also just check for a local data network cabling company. Just tell them you want them to run a shielded category 5 cable run from point "A" to "B".


Ed Vaughn, MBSWWYPBX
#259678 10/19/05 07:19 AM
Joined: Aug 2004
Posts: 1,747
Likes: 49
Admin
*****
Admin
*****
Joined: Aug 2004
Posts: 1,747
Likes: 49
Ed, why the shielded cable? The circuit is just running across Cat 3 telco/house cable to that point anyway. Up here they just extend the circuit from the CSU on house tie cable.


[Linked Image from web.atcomsystems.ca]
Looking for a VoIP Phone Canada provider? Put Atcom's valuable VoIP expertise to work for your business today!
#259679 10/19/05 07:30 AM
Joined: Jan 2005
Posts: 15,402
Likes: 18
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,402
Likes: 18
I have seen the circuits run on house pairs BEFORE the circuit terminates on the telco's termination electronics, but on the output (conditioned) side of it, there are strict limits in the distance that the wiring can go. Usually, this limit is determined by the "line buildout" settings in the electronics. I was making the assumption that they have their electronics located in the basement where the wire run would be lengthy.


Ed Vaughn, MBSWWYPBX
#259680 10/19/05 10:30 AM
Joined: Oct 2005
Posts: 160
Member
Member
Joined: Oct 2005
Posts: 160
Typical T1 distance limitations from the smartjack are a little over 600 feet. 650 pops into my head, but that's probably lab conditions.

We typically use unshielded Cat 5, 568B on both ends, and rarely have trouble. I have seen instances where screened (foil around all 4 pairs) Cat 5 was needed, and even a rare circumstance where real, honest-to-goodness sheilded (each pair in its own shield) cable was required.

#259681 10/19/05 07:17 PM
Joined: Aug 2004
Posts: 1,747
Likes: 49
Admin
*****
Admin
*****
Joined: Aug 2004
Posts: 1,747
Likes: 49
OK, so how would you know if you had cable problems between the "smart jack" and the telephone equipment?


[Linked Image from web.atcomsystems.ca]
Looking for a VoIP Phone Canada provider? Put Atcom's valuable VoIP expertise to work for your business today!
#259682 10/20/05 03:19 AM
Joined: Jan 2005
Posts: 15,402
Likes: 18
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,402
Likes: 18
Well, although the answer to your question would appear to be obvious, I see what you are saying. Obviously, a simple continuity tester would rule out any blatant wiring problems. I think what you are getting at though; it's those phantom problems that can occur and you want to rule out a wiring issue. Unfortunately, that's not quite as simple and would require the use of T1 test equipment to isolate.

It sounds scary and expensive, but I can honestly say that we have never (knock on wood)had problems with extended wiring we have installed for this purpose.


Ed Vaughn, MBSWWYPBX
#259683 10/20/05 02:49 PM
Joined: Nov 2004
Posts: 524
Member
Member
Offline
Joined: Nov 2004
Posts: 524
Run a Cat5 certification on your work. If it passes the wire map & bandwidth test, your link is good.


ElectSys Tech LLC
Hosted Phone Systems Solutions Provider
Allworx, Sangoma, FreePBX
Telephone & computer systems in the Jefferson City, Columbia MO area.
#259684 10/20/05 06:11 PM
Joined: Mar 2001
Posts: 3,869
Member
****
Member
****
Joined: Mar 2001
Posts: 3,869
How far from the MPOE is your switch? You're probably not on the 50th floor of a building where the MPOE is in the basement. That said, some old house cable we had on a job was so bad that we ran new cat 5e from the 22nd floor to the MPOE.

Well actually the CLEC ordered the LEC to extend it to the suite and the LEC could not make it work on the house cable and we ran the cable and left it for him to terminate on both ends so he had that liability. That was a first out of probably a hundred T installs but it happened.

Who knows, but if it was a long run and you ran CAT 6 would that not have less loss?

Your Adtran Ace is designed to compensate for line loss, the dip switches are there but we have never needed to use them.


THE Bracha, old blond specialist in Rube Goldberg solutions.
#259685 12/16/05 12:14 PM
Joined: Feb 2005
Posts: 63
Member
Member
Offline
Joined: Feb 2005
Posts: 63
I spoke with a verizon t1 tech and he said you can get over 1000 feet easy if you seperate the transmit and recieve pairs away from each other.. this is what cuases the 600 feet limit..


Contract SQL/C# Developer / Network Engineer
#259686 12/26/05 05:11 AM
Joined: Aug 2005
Posts: 17
Member
Member
Offline
Joined: Aug 2005
Posts: 17
I have extended T-1’s and PRI’s on cat3, cat5, cat5e, and cat5e shielded. I did however want to add to this thread that most cabling manufacturers make a specific cable for this application. If the customers are willing to pay, this is what we will always offer first, and in some instances (extensions over a few hundred feet,) it is all we will offer. Basically the cables designed for T-1 demarc extension have the pairs individually shielded. This fact is more important than the category of the cable.

Here is an example:
https://www.quabbin.com/finder/finder.cgi?cmd=display&cable_id=460

If the link does goes bad it is made by Quabbin...part number 9719

Also in Berk-Tek, part number 10032390

#259687 12/26/05 06:43 AM
Joined: May 2002
Posts: 17,746
Likes: 37
Member
****
Member
****
Joined: May 2002
Posts: 17,746
Likes: 37
When T-1's were first being installed you had to use the shielded cable. I think that is now a thing of the past, at least as far as practice goes. I would have to agree that an extended DEMARC beyond a hundred feet or so, that it would be smart to use the shielded to cut down on electronic interference


Retired phone dude
#259688 12/26/05 10:33 PM
Joined: Dec 2002
Posts: 341
Member
Member
Offline
Joined: Dec 2002
Posts: 341
I just got done running 50-pair for a 725' demarc extension yesterday. I need to extend the T-1, too (which will be a similar distance). What I'm gathering from this thread is that I can PROBABLY get away with CAT5E and perhaps some engineering inpur on the line buildout. Is this a correct assumption? Customer has been offered chance to use shielded cable and declined. I shouldn't have any unusual EMI issues on my cable path. Thanks.

Bill

#259689 12/27/05 03:20 AM
Joined: May 2002
Posts: 17,746
Likes: 37
Member
****
Member
****
Joined: May 2002
Posts: 17,746
Likes: 37
That's quite a ways. Fortunately a T1 is more tolerant of low levels than hot, also a good CSU should have some gain you can build into it. If you've offered shielded and they declined, just make sure they are well aware that it may not work as expected. The shield was as much for keeping bleed over from the transmit receive path as for EMI, for that distance I'd sure push the shield.


Retired phone dude
#259690 12/28/05 06:20 AM
Joined: Jul 2003
Posts: 766
SST Offline
Member
Member
Offline
Joined: Jul 2003
Posts: 766
Give the 50 pair a chance. Split the tx and rx between the bundles and don't forget to adjust the CSU line build-out. I'll assume you don't have a t-berd or other t1 tester so, have the service provider do a complete loop test to a CSU loop not just a 'hard loop' on the end of the wire pairs. A hard loop doubles the the length of the copper giving more line loss viewed by the tester. A 'head to head' test would be the best test but a 'soft loop' to the CSU should test fine.

#259691 12/28/05 08:34 AM
Joined: Oct 2005
Posts: 160
Member
Member
Joined: Oct 2005
Posts: 160
Don't forget to see if the LEC tech will adjsut the LBO on the smartjack. Let us know what happens.

#259692 01/04/06 01:15 PM
Joined: Aug 2005
Posts: 145
Member
Member
Joined: Aug 2005
Posts: 145
Just truned up a t1 from at&t that Verizon installed. Guess what, the trans and recieve were reversed from what they (verizon)told me. What a mess. They did the samething on the data t1. :bang:


businesstelephoneofpa.com

Planing your phones future is our business.
#259693 01/04/06 11:47 PM
Joined: Dec 2002
Posts: 341
Member
Member
Offline
Joined: Dec 2002
Posts: 341
T-1 extension came out to 740'; went live yesterday. So far, so good, but we'll wait until we get some traffic to call it good!

#259694 01/05/06 02:28 AM
Joined: May 2002
Posts: 17,746
Likes: 37
Member
****
Member
****
Joined: May 2002
Posts: 17,746
Likes: 37
Thanks for the update. If you stressed it with no problem it should have no trouble carring traffic.
Bill


Retired phone dude
Page 2 of 2 1 2

Moderated by  Silversam 

Link Copied to Clipboard
Newest Topics
Inter-Tel Axxess - Change IP's?
by alphagsc - 05/14/25 08:18 PM
Identify a 1980's reception console
by Toner - 05/08/25 01:02 PM
outdial message notification cuts off
by Bellhanger - 05/05/25 10:05 AM
3515 vodavi phones.
by Gary S. - 05/01/25 12:26 PM
Forum Statistics
Forums84
Topics94,527
Posts640,019
Members49,852
Most Online5,661
May 23rd, 2018
Newest Members
Marcgyver, DEN2MM, ferhat_efe, utec, MoverDub
49,852 Registered Users
Top Posters(30 Days)
Toner 3
Who's Online Now
1 members (jacktel), 134 guests, and 53 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998 - 2025
Powered by UBB.threads™ PHP Forum Software 8.0.0