I am running cat6 cable at a job. I was wondering if anyone knows how many calbes can be put into a 3/4", 1", and 4" pvc conduit that the electrician is piping in for me. Heading into my closet I will have about 160 cables. He is proposing 2-4" conduits. Will that be enough?

p.s. Where can I find documentation on this?

Thanks,

Doubled

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#442219 02/15/05 01:15 PM
Joined: Sep 2004
Posts: 1,436
Member
Offline
Member
Joined: Sep 2004
Posts: 1,436
I've got 98 cat5 cables split between 2 1.5" conduits, so 2 4" should handle it with room to spare. The only thing I know would be to start shoving cable into a piece of conduit and see how many will fit.


Joe
---
No trees were harmed as a result of this posting; however, many electrons were severely inconvenienced.
#442220 02/15/05 01:28 PM
Joined: Oct 2004
Posts: 684
Member
Offline
Member
Joined: Oct 2004
Posts: 684
The National Electric Code book is where you would find that info. An inspector once told me not more than half full, but would allow 3/4.

#442221 02/15/05 01:33 PM
Joined: Dec 2004
Posts: 233
doubled Offline OP
Member
OP Offline
Member
Joined: Dec 2004
Posts: 233
Thanks for the help guys. I know the code book says that you can only fill a conduit 60% full (MN), but I found out that the inspector doesn't worry so much about that as to making sure all of my cables are tied up by their own supports.

#442222 02/16/05 04:02 PM
Joined: Sep 2004
Posts: 1,436
Member
Offline
Member
Joined: Sep 2004
Posts: 1,436
How long are the conduits? If only going through a wall, you can fill them completely. Going very far, use 50-60% fill maximum or it will be really hard to pull and you could damage the cables. If I remember, the codebook says 50% fill to limit heat buildup from current-carrying wires.


Joe
---
No trees were harmed as a result of this posting; however, many electrons were severely inconvenienced.
#442223 02/17/05 02:33 AM
Joined: Oct 2001
Posts: 4,043
Member
Offline
Member
Joined: Oct 2001
Posts: 4,043
Also dn't forget to allow for any future runs
and no more then 3 90s per run.
Add any 45s or kicks also.
It's a real PITA to get 80 or 100ft of cable into a pipe only to find the EC didn't use a bender or install the couplings properly.
You'll find yourself breaking the pipe in the middle of the run. [Linked Image from sundance-communications.com]

#442224 02/17/05 12:54 PM
Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Offline
Member
Joined: Dec 2004
Posts: 5,722
You're all right ---- maybe. TIA 568 and the NEC give the support and fill rates. The average (depending on the size of the wire) into the face surface is the figure. Even though the NEC calls for current load bearing conductors the TIA 568 follows the same as electrical.

The average cable count per sq inch surface face for General Cable is 28. At 55% fill on a 4" you should get just over 160 per pipe. Get the wire specs from your vendor,
figure your sq inches of pipe face ( size X 3.14) divide by fill rate (schedule by pipe size in NEC/ TIA) times the size/number of wires in one sq inch. Confusing? Oh Yeah !! Had to do it on a hospital job in Pennsylvania to make the state inspector happy. He was a rough dog to convince. He also wanted to pull our face plates to check for fire stop --- didn't want to be charged for re-certifaction.

Sorry to be long winded but the inspector is ALWAYS right.


Ken
---------
#442225 02/18/05 03:18 PM
Joined: Jun 2004
Posts: 4,552
Moderator-Comdial, ESI, Voicemail, Cisco
Offline
Moderator-Comdial, ESI, Voicemail, Cisco
Joined: Jun 2004
Posts: 4,552
Explain a little more on the fire stops behind the faceplates. Aren't the faceplates themselves fire-rated? Are you talking about around the actual box?

Don't you hate it that the inspector is always right, even when they are dead wrong?

#442226 02/18/05 04:02 PM
Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Offline
Member
Joined: Dec 2004
Posts: 5,722
5 Year, oh are you so right.

The fire stop issue was the box was cut into the fire wall between the patient room and the hall way. Metallic flexible conduit was run inside the wall and out into the hallway ceiling. This penetration of the fire envelope required the flex to be firestopped where it entered the box in the room and a knot of fire stop at the top of the flex where it entered the cable tray thus sealing the pathway.

I thought the city inspector in Philly was rough ---- you should have seen the State Fire Marshall inspection !!!!
The inspector had one eyebrow ----- over one eye, one broken fang, and raw knuckles from dragging on the sidewalk ---- he was a REAL pain. He got whatever he wanted !!!!


Ken
---------
#442227 03/18/05 09:06 AM
Joined: Mar 2005
Posts: 97
Member
Offline
Member
Joined: Mar 2005
Posts: 97
Now in Wisconsin, in certain applications including hospitals, you have to pack the backsides of the boxes in 2 hour rated firewalls even if you do not penetrate to another space. What a pain.


Moderated by  Silversam 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,262
Posts638,696
Members49,757
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,098 Shoretel
187,710 CTX100 install
186,795 1a2 system
Newest Members
BPopilek, Rich F, LewisR, TDKs79, Buttinset
49,757 Registered Users
Top Posters(30 Days)
dexman 18
Toner 11
TDKs79 8
jc2it 4
teleco 4
Who's Online Now
1 members (Toner), 163 guests, and 239 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5