Simple (probably stupid) question. How or what am I suppose to ground my server rack to the 2-3 inch copper strip on the floor near the baseboard leading to my AC outlet in the Server Room.
The 4-post rack is bolted to the floor. Does that mean my rack is already grounded to that strip running underneath the laminated tile? Or am I suppose to run a wire to that copper strip? Do i need a "grounding bar" instead?
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
I really cannot completely understand what this looks like. It sounds to me like if there is a ground bus then I would bond my rack to it and not rely on the bolts holding it down.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Jul 2001
Posts: 3,347 Likes: 10
Moderator-Avaya-Lucent, Antique Tele
|
Moderator-Avaya-Lucent, Antique Tele
Joined: Jul 2001
Posts: 3,347 Likes: 10 |
The only copper strips I have seen in telephone / computer rooms are grounding the conductive linoleum. You still need a grounding bar provided by the electrician.
|
|
|
|
Joined: May 2008
Posts: 10
Member
|
Member
Joined: May 2008
Posts: 10 |
I will post a picture, hang tight guys. Thanks for responding.
|
|
|
|
Joined: Dec 2004
Posts: 5,722
Member
|
Member
Joined: Dec 2004
Posts: 5,722 |
Touch Tone Tommy hit it on the head. The strips going from the floor to the electical outlet is a static discharge strip for the anti-static flooring. Get your electrician to place a proper grounding bar for you to ground ALL your racks and equipment to.  :thumb: :banana: 
Ken ---------
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
The EIA/TIA 607 spec covers Grounding & Bonding for Data Centers.
Please note that this has NOTHING to do with the NEC Grounding requirements - those are grounding for safety - these are grounding for performance.
If you haven't got the $1000+ for the EIA specs, check out Panduit's 'StructuredGrounding' system. It'll give you a good idea of how to ground & bond data centers. (A little overkill perhaps, but better over then under).
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
The strips going from the floor to the electical outlet is a static discharge strip for the anti-static flooring.
Yup, that's why those bolts through the floor aren't doing anything. The floor is semi-conductive and the copper does not extend under it. The floor itself has a high resistance.
-Hal