Ladies and Gentleman, especially certified electricians:
Due to many KSU power supplies failing, I believe in addition to the grounding prong of the KSU power cord that we should also be installing a direct ground wire to the cabinet.
I would appreciate all EXPERT opinions on this.
Thank you.


Telesystems technician
Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Jun 2006
Posts: 8,732
Likes: 2
Moderator-Nortel, Computers, General
*****
Offline
Moderator-Nortel, Computers, General
*****
Joined: Jun 2006
Posts: 8,732
Likes: 2
Have to disagree with you. Most Nortel KSU do NOT have a connection point for that.

I believe it is because when their 1st electronic KSU's came out (the Vantage series), I was still at Bell. Bell was having a problem with KSU's blowing from lightning so they commissioned several of their "top-notch" PBX Repair Techs to do a province wide (maybe even a country-wide) study comparing results of those that were & were NOT grounded.

Apparently they found little difference if any as to the potential risk, with or without being grounded.

I'm sure few will agree with me but in my experience I've only had to change one KSU that was a known lightning hit.


Scientists say that the universe is made up of Protons, Neutron & Electrons. They forgot "Morons".
Dave. (CTUB) Canadian Techs Use Bix!
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Online Content
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
The biggest mistake made in grounding is your equipment being a different ground potential than the electrical. That's why most use the third prong only. You never want to be the best or worst ground source.


Retired phone dude
Joined: Jan 2013
Posts: 519
Likes: 1
Member
Offline
Member
Joined: Jan 2013
Posts: 519
Likes: 1
First question I need to ask is why are they failing so much? Bad design or an external event causing the failure.

Nothing you can do about a bad design, but you can do lots about external events causing them to fail.

Do you have them plugged into a good surge suppressor/line filter and or a good UPS that supplies the same?

Have you checked the voltage and current between ground and neutral to see if you have a bonding issue or such?


Patrick T. Caezza
Santa Paula, CA 93060
C-7 - Low Voltage System Contractor - Lic# 992448
Joined: Dec 2008
Posts: 510
Member
Offline
Member
Joined: Dec 2008
Posts: 510
Would their be warranty issues with manufacturers on failed systems that haven't been grounded via their grounding lug.


Bob

With all the variables involved, I am amazed when any voice and data technology works like it is supposed to.
Joined: Apr 2009
Posts: 194
Member
OP Offline
Member
Joined: Apr 2009
Posts: 194
Ground potential is a major concern. I just had two IP office telephone sets go down after a storm.
Note: Almost everything is now made in CHINA.
The Chinese make mistakes in their electrical engineering designs
e.g. back up power supplies.


Telesystems technician
Joined: Jun 2006
Posts: 8,732
Likes: 2
Moderator-Nortel, Computers, General
*****
Offline
Moderator-Nortel, Computers, General
*****
Joined: Jun 2006
Posts: 8,732
Likes: 2
No matter what you do you can't do it all.

Example: When I was with Bell, we had issues with our computer. The computer center in Montreal told us to call \our local Building dept. Called the Building Dept and they put a line recorder on the electrical outlet for a week. Nothing. Then we called the "CCNS" dept (data group) who put on a $50000 test set & within 3 04 4 minutes they had found the problem. Voltage was all over the map between 80 and 145 volts for just parts of a second.

Hydro Quebec had to get involved.






Scientists say that the universe is made up of Protons, Neutron & Electrons. They forgot "Morons".
Dave. (CTUB) Canadian Techs Use Bix!
Joined: Dec 2005
Posts: 9,162
Likes: 8
Spam Hunter
*****
Offline
Spam Hunter
*****
Joined: Dec 2005
Posts: 9,162
Likes: 8
If an external ground is desired...and the AC outlet that provides power to the system has been checked and tested...consider using a grounding block. Plug the key system into the block and plug the block into the electrical outlet. The block should provide a suitable ground point for the telephone system.

Joined: Feb 2005
Posts: 12,342
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,342
Likes: 3
Originally Posted by justbill
The biggest mistake made in grounding is your equipment being a different ground potential than the electrical. That's why most use the third prong only. You never want to be the best or worst ground source.

That's absolutely correct. If you ground the system and/or rack you always want to make sure there is no voltage difference between the ground prong on the line cord and whatever ground you are using. Only way to insure that is to bond to the electrical receptacle. I have actually had systems destroyed because of a voltage between the power cord ground and where I had the system ground connected. And incidentally, the ground screw on KSUs is only there to satisfy UL who requires that the premises wiring through the KSU be grounded in the event that the line cord is disconnected from the receptacle.

Originally Posted by Telesystems
Ground potential is a major concern. I just had two IP office telephone sets go down after a storm.

I seriously doubt that the phone damage had anything to do with grounding. Over the years I have seen ethernet ports on various equipment as well as TDM phones and the associated ports on the KSU destroyed be lightning. It's because the EM pulse from the lightning induces a voltage on the cable itself. Only thing that will help with that is transient suppressors at both ends of the cable that are grounded properly.

-Hal

Joined: Oct 2010
Posts: 250
Member
Offline
Member
Joined: Oct 2010
Posts: 250
Question: Isn't the the green ground wire in the power cable harness also tied to frame ground inside the electronic KSU cabinet?






Forty six years and still fascinated with Telecommunications!
Page 1 of 3 1 2 3

Moderated by  MooreTel 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,262
Posts638,696
Members49,757
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,098 Shoretel
187,707 CTX100 install
186,794 1a2 system
Newest Members
BPopilek, Rich F, LewisR, TDKs79, Buttinset
49,757 Registered Users
Top Posters(30 Days)
dexman 18
Toner 14
TDKs79 8
Who's Online Now
2 members (Toner, justbill), 117 guests, and 243 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5