This customer has had a paging system in place for many, many years. Some of the horns I installed, some by others (and they used a different speaker). I replaced the Bogen TPU60 5 years ago, because it had quit working after the previous 2 decades. The company plays background music through the system, and overhead pages when needed.
During the last couple of weeks, the amp has tripped it's built-in reset breaker. By the time I get there, I can't tell if the amp was hot or not. They claim no one has done any wiring or added any speakers. Resetting the reset breaker and everything works for a few days or a week, until it trips again.
I don't have an impedance meter, nor know how to use one. The wiring is old and mostly in a moist greenhouse environment. It splits off here and there a couple of places. It will be a nightmare to trace out and test. But what am I looking for? Reading each leg with an ohmmeter for shorts, high opens, ???
I'm thinking a bad horn or corroded wiring/connection?
Thanks for any direction. Jim
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Jan 2007
Posts: 1,027
Member
|
Member
Joined: Jan 2007
Posts: 1,027 |
An impedance meter is really the way to go. The Tpu 60 is a 60 watt amp you said they have horn speakers are they SPT 15's or something similar? Is it possible someone upped the wattage draw on the speakers? I've seen customers up the Spt 15's to the max of 15 watts is that possible? Does it trip after they make a page or just randomly shuts down? Are you wired for 25 or 70 volts?
John 807
|
|
|
|
Joined: Jan 2010
Posts: 223 Likes: 1
Member
|
Member
Joined: Jan 2010
Posts: 223 Likes: 1 |
If you know how to use a DMM, you know how to use an impedance meter. Without the impedance meter and a ground fault check, you can't eliminate the amplifier itself as the problem. Yes you will be looking for short circuits, ground faults, and overloaded lines (although this requires the impedance meter). Is there any hum or noise on the BGM source?
|
|
|
|
Joined: Jul 2006
Posts: 2,756 Likes: 21
Admin
|
Admin
Joined: Jul 2006
Posts: 2,756 Likes: 21 |
I vaguely remember, back in the K-Mart days, we used to find that some rogue employee would think they knew how to install speakers. Two wires, right? Or, worse, the black tape instead of speaker nuts would come loose and ground itself to the ceiling grid.
As the others have said, an ANALOG impedance meter is a nice tool to own. Turning up the volume (a Pyle PCM60 runs less than $100 on the secondary market or you could drive to Ohio and take an amp or two off my shelf). The problem is that you want to equip yourself with all the tools before you go to the job, or be very close to the site. Without that, look for corrosion in your moist environment and try to cut the load in half. Once you lift the speakers from the grid, you can meter them to ground and look for low resistance faults to ground on the legs you split off. You may find an odd resistance reading that doesn't match the others. Or, you'll probably find that bad boy in the middle of your string :-)
Good luck.
BTW the new amps actually have Bluetooth receivers and MP3 inputs for BGM and MOH.
Carl
This model is end of life
|
|
|
|
Joined: Feb 2005
Posts: 12,353 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,353 Likes: 4 |
I really doubt that an output short or other lesser problem would cause the circuit breaker to trip. That amplifier has electronic protection for that. Considering that the amp probably isn't used to its full 60W capacity with playing background music and probably not even during a page anyway, a short would only result is a loss of audio.
The circuit breaker is in series with the like AC line cord to protect against major problems like power transformer failure, output transistor failure, etc. So, my thoughts are that the circuit breaker itself is defective or there is some intermittent problem with the amp.
Time for a new amp unless you are competent to try replacing the circuit breaker.
-Hal
Last edited by hbiss; 02/17/25 08:32 PM.
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: May 2002
Posts: 17,742 Likes: 32
Member
|
Member
Joined: May 2002
Posts: 17,742 Likes: 32 |
I agree with Hal, especially if the breaker is an arc fault breaker.
Retired phone dude
|
|
|
|
Joined: Feb 2005
Posts: 12,353 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,353 Likes: 4 |
No Bill, it's the breaker on the amp that keeps the magic smoke from escaping.  -Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Oct 2006
Posts: 1,415 Likes: 6
Member
|
Member
Joined: Oct 2006
Posts: 1,415 Likes: 6 |
Right, Hal. Little red reset button.
If it's regular solder pads, I can handle that, provided I can find the correct replacement part.
If it's the new surfacemount solder, I'm sol.
Jim
|
|
|
|
Joined: May 2002
Posts: 17,742 Likes: 32
Member
|
Member
Joined: May 2002
Posts: 17,742 Likes: 32 |
Sorry about that, guess reading isn't my best subject. I still hate arc fault breakers.
Retired phone dude
|
|
|
|
Joined: Oct 2006
Posts: 1,415 Likes: 6
Member
|
Member
Joined: Oct 2006
Posts: 1,415 Likes: 6 |
No problem, Bill. FWIW, I'm not a fan of arc fault either, but a necessary evil.
|
|
|