Posted By: ATechguy Grounding 25 pr. circa protection? - 10/14/08 04:55 PM
HI! Again , quick question to the pros if the building electical goes to main water pipe and i am 120 ft. away from main ground, can i find a closer water pipe to run a # 6 gound for the circa protection?? Or do i have to run a large cooper wire to main ground in electrial room??The building trusses are not grounded. eek
Posted By: hbiss Re: Grounding 25 pr. circa protection? - 10/14/08 05:16 PM
Drive an 8'x5/8" ground rod at the protector location. From the protectors and that ground rod run a #4 copper ground conductor back to the electrical room.

-Hal
Posted By: EV607797 Re: Grounding 25 pr. circa protection? - 10/14/08 05:26 PM
Well, I'm not sure of the Canadian Electrical Code requirements, but I'm fairly confident that they are similar to those in the US.

IF, (and I mean that you will need to confirm this) there is a 3/4" or larger copper cold water pipe that is not insulated by some form of joint or plastic piping, you will be OK. Don't forget to check for plastic water meter housings. This pipe will be a superior bonding connection to steel building framing anyway.

Otherwise, proper integrity over such a distance would require something more like a #2AWG bond to go all the way to the electric service ground. This would be necessary to overcome resistance due to distance. The proper water pipe will save you this trouble and expense.

Still, it concerns me that the metal framing members are not bonded to the electric, water and gas (if present) facilities. You might want to double-check that and if it truly is the case, you should advise the building owner of this deficiency.
Posted By: ATechguy Re: Grounding 25 pr. circa protection? - 10/14/08 05:44 PM
Thanks guys,i did talk to the original electric contractor and he did confirm the the steel beam trusses are not grounded ,this is a 1 yr. old building, So if i can find cooper piping with no non conductor joints a can use this as the cheapest solution.?? Thanks
Posted By: KLD Re: Grounding 25 pr. circa protection? - 10/14/08 06:18 PM
Watch yourself if the building is not grounded or bonded....not even cathodic protection. You don't want to become the better ground.
Posted By: Noisycow Re: Grounding 25 pr. circa protection? - 02/07/09 10:43 AM
75% of the OSP enclosures and 90% of the data racks I see here are not grounded at all.

Trying to put together a 'grounding kit' right now so we have what we need on hand at any job, hopefully. Can't depend on, or wait for, a sparkie to provide a ground.
Posted By: Silversam Re: Grounding 25 pr. circa protection? - 02/07/09 02:16 PM
Noisycow -

Recognize that there are 2 kinds of grounding:

1 - for safety
2 - for performance

For safety related grounding refer to the NEC

For performance related grounding refer to the EIA/TIA 607 spec. Panduit also has a nice set of grounding equipment and practices for data centers and the like.

Sam