HI! Again , quick question to the pros if the building electical goes to main water pipe and i am 120 ft. away from main ground, can i find a closer water pipe to run a # 6 gound for the circa protection?? Or do i have to run a large cooper wire to main ground in electrial room??The building trusses are not grounded. eek

EMP & Lightning Home Surge Protection
EMP - Click Here!
Re: Grounding 25 pr. circa protection?
#474741 10/14/08 05:16 PM
Joined: Feb 2005
Posts: 12,249
Member
***
Online Content
Member
***
Joined: Feb 2005
Posts: 12,249
Drive an 8'x5/8" ground rod at the protector location. From the protectors and that ground rod run a #4 copper ground conductor back to the electrical room.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Re: Grounding 25 pr. circa protection?
#474742 10/14/08 05:26 PM
Joined: Jan 2005
Posts: 15,231
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Online Content
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,231
Well, I'm not sure of the Canadian Electrical Code requirements, but I'm fairly confident that they are similar to those in the US.

IF, (and I mean that you will need to confirm this) there is a 3/4" or larger copper cold water pipe that is not insulated by some form of joint or plastic piping, you will be OK. Don't forget to check for plastic water meter housings. This pipe will be a superior bonding connection to steel building framing anyway.

Otherwise, proper integrity over such a distance would require something more like a #2AWG bond to go all the way to the electric service ground. This would be necessary to overcome resistance due to distance. The proper water pipe will save you this trouble and expense.

Still, it concerns me that the metal framing members are not bonded to the electric, water and gas (if present) facilities. You might want to double-check that and if it truly is the case, you should advise the building owner of this deficiency.


Ed Vaughn, MBSWWYPBX
Re: Grounding 25 pr. circa protection?
#474743 10/14/08 05:44 PM
Joined: Nov 2006
Posts: 701
Member
OP Offline
Member
Joined: Nov 2006
Posts: 701
Thanks guys,i did talk to the original electric contractor and he did confirm the the steel beam trusses are not grounded ,this is a 1 yr. old building, So if i can find cooper piping with no non conductor joints a can use this as the cheapest solution.?? Thanks

Re: Grounding 25 pr. circa protection?
#474744 10/14/08 06:18 PM
Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Offline
Member
Joined: Dec 2004
Posts: 5,722
Watch yourself if the building is not grounded or bonded....not even cathodic protection. You don't want to become the better ground.


Ken
---------
Re: Grounding 25 pr. circa protection?
#474745 02/07/09 10:43 AM
Joined: Sep 2007
Posts: 1,173
Member
Offline
Member
Joined: Sep 2007
Posts: 1,173
75% of the OSP enclosures and 90% of the data racks I see here are not grounded at all.

Trying to put together a 'grounding kit' right now so we have what we need on hand at any job, hopefully. Can't depend on, or wait for, a sparkie to provide a ground.

Re: Grounding 25 pr. circa protection?
#474746 02/07/09 02:16 PM
Joined: May 2007
Posts: 4,973
Moderator-1A2, Cabling
*****
Offline
Moderator-1A2, Cabling
*****
Joined: May 2007
Posts: 4,973
Noisycow -

Recognize that there are 2 kinds of grounding:

1 - for safety
2 - for performance

For safety related grounding refer to the NEC

For performance related grounding refer to the EIA/TIA 607 spec. Panduit also has a nice set of grounding equipment and practices for data centers and the like.

Sam


"Where are we going and why are we in this hand basket?"

Moderated by  EV607797, Professor Shadow 

Link Copied to Clipboard
Forum Search
Most Recent 5 Post
Unisons to give away
by RUSS K. - 09/21/20 01:52 AM
problem with a new CO line on a Panasonic KX-T30810
by LenShustek - 09/20/20 09:55 PM
Issue with tenants/trunk groups
by EV607797 - 09/20/20 07:46 PM
CenturyLink Rebrands Three Ways.
by dexman - 09/19/20 10:44 PM
SV 9100 CP 10
by teldata1 - 09/18/20 05:10 PM
Who's Online Now
23 members (nortelvoip, Meyery2k, EV607797, Mercenary Roadie, pvj, BobRobert, hbiss, newtecky, LenShustek, RUSS K., Professor Shadow, RATHER BE FISHING, Tip&Ring, Touch Tone Tommy, C5Z, hitechcomm, Hofman telekom, Bob3470, metelcom, Yoda, justbill, teldata1, Ruben), 190 guests, and 45 robots.
Key: Admin, Global Mod, Mod
Popular Topics (Views)
Forum Statistics
Forums94
Topics93,953
Posts637,232
Members49,346
Most Online5,661
May 23rd, 2018
Today's Birthdays
boots921, Don Mynes, glennlandrew, leonard kryston, maninquestion, roky4rach
Newest Members
Ray Mar, NKol423, Rob McKay, s0397, Craypaz
49346 Registered Users
Get Tech Support Now! Click the banner below
Get Tech Support Now!
Top Posters (30 Days)
dexman 31
teleco 12
hbiss 9
ABLE1 7
Bluewater Sailing
https://www.patreon.com/bePatron?u=5256033
EMP Shield for Commercial - Home & Vehicle
Use Coupon code SAVE - Click Here!
Servpro Ventura 24-Hour Emergency Service
Free Estimates call us now 24Hours
Contact Us | Telephone System Tech Support | Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers.
©Copyright Sundance Communications 1998-2020
Trusted Partners