Oh, and I should mention (or ask) what's going to happen when CAT5e is no longer available and replaced by CAT6? That's even more money and it makes no sense to use it where it is not needed.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Aug 2001
Posts: 774
Member
|
Member
Joined: Aug 2001
Posts: 774 |
Any company knows that PVC cable is cheaper than Plenum cable. I do know 99% of the time what is required in each city, Town, and county in the DFW area of Texas. A signed letter protects me from running PVC cable, and the city inspector saying that it has to be removed and replaced, BY ME, to be within what he reads as code. Now, even in that 1% I may be right, but by the time I prove it to the city, my customer has missed his move in date, due to me. So as I said " I will NEVER run PVC cable without a signed letter from my customer." The letter basicly states that the customer is requesting PVC cable to be installed in there work area, and has been advised by my company that this may not be to code for the area and for the type of building or ventalation. Signed by upper level management on there company letter head. CAT 5e will never be totally replaced by CAT 6, just as CAT 3 has not been replaced (CAT 3 was origanally for 10BaseT) ------------------ Voice and Data Cabling in DFW, [email protected] DnR Communications
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
CAT 5e will never be totally replaced by CAT 6, just as CAT 3 has not been replaced (CAT 3 was origanally for 10BaseT)
What happened to CAT5? And I actually remember a CAT4, it lasted for about a year. CAT 3 has a use- it's the minumum required for voice. When CAT6 becomes the minimum for data nobody will make CAT5e anymore.
Any company knows that PVC cable is cheaper than Plenum cable.
Funny thing is that in all my years in business I have never had a customer even ask about this. Sure, they want to know if it's CAT5 or CAT5e but as for whether it is plenum rated or not all the want to know is if it meets code, and they rarely even mention that.
Every proposal and contract I write states that the work will be done in accordance with all applicable codes. If the customer wants me to violate the code I don't need a letter, they can go someplace else.
Obviously where you are there is no licensing, because letter or no letter YOU would be responsible.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Aug 2001
Posts: 774
Member
|
Member
Joined: Aug 2001
Posts: 774 |
<font face="Verdana, Arial" size="2">Originally posted by hbiss: CAT 5e will never be totally replaced by CAT 6, just as CAT 3 has not been replaced (CAT 3 was origanally for 10BaseT)
What happened to CAT5? And I actually remember a CAT4, it lasted for about a year. CAT 3 has a use- it's the minumum required for voice. When CAT6 becomes the minimum for data nobody will make CAT5e anymore.
Any company knows that PVC cable is cheaper than Plenum cable.
Funny thing is that in all my years in business I have never had a customer even ask about this. Sure, they want to know if it's CAT5 or CAT5e but as for whether it is plenum rated or not all the want to know is if it meets code, and they rarely even mention that.
Every proposal and contract I write states that the work will be done in accordance with all applicable codes. If the customer wants me to violate the code I don't need a letter, they can go someplace else.
Obviously where you are there is no licensing, because letter or no letter YOU would be responsible.
-Hal
</font> No need to reply to this. ------------------ Voice and Data Cabling in DFW, [email protected] DnR Communications
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
No need to reply to this.
Why is that??
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Jan 2005
Posts: 15,397 Likes: 18
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,397 Likes: 18 |
Some of you contractors out there may have the luxury of using plenum cable everywhere. Unfortunately, that's not always legal but is not being enforced by local officials. It is being enforced here, if just a technicality. Reinspections result in additional revenue for the city or county. You can imagine how I feel about this.
You see, most plenum rated cable has excellent low-smoke producing properties in a HORIZONTAL environment, but has awful properties when installed in a VERTICAL installation. Some plenum jacket materials are actually more flamable when installed vertically than riser-rated (CMR) cable.
The National Electrical Code states that all materials used "shall be approved for the purpose". Type CMP cable (plenum) is traditionally approved for use in plenum spaces. Recently, most manufacturers have changed their jacket formula to be accepted in horizontal plenum or vertical (riser) applications but that's not universal practice by all manufacturers, nor is it mandatory.
Still, just because plenum cable costs more than PVC (non-plenum) doesn't mean it can be used everywhere. Cost is not what determines compatibility; it's how it is rated by Underwriter's Laboratories or accepted by your local authority having jurisdiction (AHJ).
Bottom line: CMR (riser-rated) cable doesn't burn well when installed vertically but it burns like crazy in a horzintal environment;
CMP (plenum-rated) cable doesn't burn much when installed horizontally but goes up in flames when installed vertically.
Technically, it's not legal to wire a single family residence, townhouse, etc. with type CMP (plenum) cable, just like it's not legal to run type CMR (riser) cable in a plenum ceiling.
Those of you out there using CMP cable for everything might be enjoying the convenience of stocking only one type of cable, but a sharp electrical inspector might come along and change your way of thinking.
So you asked, how do I know so much about this? We have strict requirement to prove NEC knowledge (through verified continuing education credit courses) each year when our 30+ licenses are renewed.
We had to rewire an addition to a hospital plus another job involving 130 residential condiminiums a few years ago because the installation DID NOT require the use of plenum-rated cable where we had installed it. We thought by using the most expensive cable, we were safe. We failed inspection. This was due to the fact that the wiring wasn't installed within air return plenums. In these cases, the National Electrical Code's "material approved for the purpose" mandated that since the wiring wasn't in an air return plenum environment, plenum (CMP) cable wasn't the material approved for the purpose. It was cheaper to replace it than to fight the inspector.
Most manufacturers have had their plenum-rated cable models dual-rated now, but you might not ever know if you are using an older model. We found out that some of the cable we just received last month is still not dual-rated.
Again, more expensive isn't always better.
We run miles of CAT3 for voice annualy and unless otherwise mandated, that's our norm. As for data, the customer calls that shot. Still, we always verify if it's a plenum environment......The NEC seems to be trying to keep us from spending money on CMP when not necessary. No problem here!
------------------ Ed --------- How come there's always enough time to go back and fix it a second time?
[This message has been edited by ev607797 (edited July 02, 2005).]
[This message has been edited by ev607797 (edited July 02, 2005).]
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Aug 2001
Posts: 774
Member
|
Member
Joined: Aug 2001
Posts: 774 |
Sorry, I was only speaking of Horizontalk Cabling, of course Vertical Cabling (Riser) is a different story. ------------------ Voice and Data Cabling in DFW, [email protected] DnR Communications
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
You see, most plenum rated cable has excellent low-smoke producing properties in a HORIZONTAL environment, but has awful properties when installed in a VERTICAL installation. Some plenum jacket materials are actually more flamable when installed vertically than riser-rated (CMR) cable.
I would like to agree with you but I can't see where you are getting your information from, certainly not from the NEC.
If you look at any of the cable hierarchy substitution tables in the NEC (for instance 800.53)you will see that a plenum rated cable is at the top of the heap and can be substituted for any of the lesser types such as riser and general purpose. There is absolutely nothing in the NEC that would prohibit plenum rated cables use in vertical runs or residential construction.
I believe your inspector is taking the descriptions of the different types of cables in 800.51 (A) through (E) literally without understanding the the substitution hierarchy which is included in every NEC article having to do with low voltage wiring.
Unless your state or jurisdiction has adopted the NEC with ammendments that would contradict this it appears from what you say that your classes are also making the same serious mistake. They wouldn't happen to be taught by the inspector would they?
Most manufacturers have had their plenum-rated cable models dual-rated now...
I just got a shipment of Commscope plenum CAT5e the other day and I don't know what you are talking about. Why would there even be a reason to dual rate a plenum rated cable? I'll check into this but I think your information is totally wrong and it seems it has cost you a lot of money.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Oct 2004
Posts: 812
Member
|
Member
Joined: Oct 2004
Posts: 812 |
I saw this on the news the other day...The compund, dupont is made famous for. Such as teflon and simular compounds in fire rated cable just might cause cancer in rats and the EPA is going after them to take it off the market. The next thing we will be doing is running steel conduit for voice and data.
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
I heard that about teflon coated frying pans years ago. Would think that cookware is more of a health concern than some cable up in the ceiling. Most current plenum rated cable is not made with teflon anyway so this is a non-issue.
What seems to be becoming a big issue is that the current jacket formulations contain lead. Seems they want to replace them with teflon...