not so good
#443499 07/05/06 09:20 PM
Joined: Dec 2002
Posts: 9,380
Member
*****
OP Offline
Member
*****
Joined: Dec 2002
Posts: 9,380
Take a look at these pics
https://www.onecallsupport.com/gall...ons&sFolder=Complete+Claim+Solutions
This was posted in another forum...due to my eye for detail I noticed the following:
1) the wires are not twisted enough from what I saw on the patch panel terminations
2) there is too much jacket removed on the workstation jack end.
3) did not see any labeling on either ends of the cables
4) in this pic, the conduit needs to have a bushing and/or a fitting depending on code.
https://www.onecallsupport.com/gallery/Complete%20Claim%20Solutions/DSCN0456.JPG
Have at it..wonder what else we can find smile
PS. on the forum the OP said this was a Cat 6 install, I saw on the jacks, cable, and panels that it was Cat 5e.
Here is the post from the other forum
https://www.dslreports.com/forum/remark,16429885~mode=flat


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
Telephone Equipment Search
Re: not so good
#443500 07/05/06 10:21 PM
Joined: Jan 2005
Posts: 15,203
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Online Content
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,203
All I can say is that a Sparkie landed a big deal by being the low bidder and wants to show off.

The pictures look a little bit better than my worst project where people were actually fired.

I am too much of a perfectionist. I have a hard time with white cable ties. They are usually cheapo imports. I insist that ours match the cable color, and we don't use white cable. In situtations where white cable is requested, sorry but telco gray for the cable ties is all I will allow.


Ed Vaughn, MBSWWYPBX
Re: not so good
#443501 07/05/06 10:50 PM
Joined: Feb 2006
Posts: 826
Member
Offline
Member
Joined: Feb 2006
Posts: 826
Great find Jeff.

I can't understand how someone could possibly be proud enough of that job to post pictures like that. The terminations look like what my students would do on their first try. And even then, most of them do a better job on the first go. This is just sad. Someone didn't spend nearly enough time dressing out their cables.

Personally, I'm moving away from using tie wraps for anything beyond the pathways. At the rack/patch panel it's all velcro. But honestly, the tie wraps are the least of the crimes being committed here.

Re: not so good
#443502 07/06/06 05:23 AM
Joined: Sep 2005
Posts: 264
Member
Offline
Member
Joined: Sep 2005
Posts: 264
If this was my building I would ask for my money back. Obviously these guys either have no pride in their work or they just stink at it. Either way, its not good.

Re: not so good
#443503 07/06/06 05:47 AM
Joined: Jun 2005
Posts: 512
Member
Offline
Member
Joined: Jun 2005
Posts: 512
The problem is, that the people that are having data wiring done for them don't realize how important it really is to a network. If you don't have the proper infrastructure or it is done poorly, it can and will affect your network as a whole. Their mind thought is that its just some wires, who cares just throw it in, so we can get to the important stuff like the hardware. :bang:

Re: not so good
#443504 07/06/06 05:56 AM
Joined: Jan 2004
Posts: 6,646
Moderator-Nisuko-Tie, General
*****
Offline
Moderator-Nisuko-Tie, General
*****
Joined: Jan 2004
Posts: 6,646
we dont nedd no steenkiiin velcro we got masking tape

https://www.onecallsupport.com/gallery/Complete%20Claim%20Solutions/DSCN0438.JPG :rolleyes:


Skip
------------------------------------

Serving SW and West central Fl since 1984
Re: not so good
#443505 07/06/06 06:00 AM
Joined: Dec 2005
Posts: 2,928
Member
Offline
Member
Joined: Dec 2005
Posts: 2,928
now that is nice..I hope that was just temporary....I don't get it, they have a bushing on the one pipe but not the other three..go figure


I Swear I did not touch anything bash
Re: not so good
#443506 07/06/06 06:35 AM
Joined: Dec 2002
Posts: 9,380
Member
*****
OP Offline
Member
*****
Joined: Dec 2002
Posts: 9,380
I looked closer because I thought I saw cable ties, but in the pictures of the ladder rack it is lacing string...
PS. That company claims to be a network/cabling specialist, too...WOW


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
Re: not so good
#443507 07/06/06 06:37 AM
Joined: Mar 2006
Posts: 575
Member
Offline
Member
Joined: Mar 2006
Posts: 575
https://www.onecallsupport.com/gallery/Complete%20Claim%20Solutions/DSCN0472.JPG

Is this their idea of a proper AC outlet?

Or this

https://www.onecallsupport.com/gallery/Complete%20Claim%20Solutions/DSCN0468.JPG

In this one, you can see that there's no box. They mounted it on a caddy, with all sorts of wires behind it, I can't even SEE any MC.

https://www.onecallsupport.com/gallery/Complete%20Claim%20Solutions/DSCN0463.JPG

On the left you see the guy's laptop. It's got his timesheet on the screen. On the right, we see the root of the problem - Cisco phones.


Rob Cashman
Customer Support Engineer
Re: not so good
#443508 07/06/06 06:37 AM
Joined: Dec 2002
Posts: 9,380
Member
*****
OP Offline
Member
*****
Joined: Dec 2002
Posts: 9,380
Oh yeah, I am waiting for the OP on the other forum to respond...I took pictures of my patch panel terminations at home to show him.


Jeff Moss

Moss Communications
Computer Repair-Networking-Cabling
MBSWWYPBX, JGAE
Page 1 of 3 1 2 3

Moderated by  Professor Shadow, Silversam 

Link Copied to Clipboard
Forum Search
Most Recent 5 Post
Suttle Apparatus Acquisition.
by dexman - 07/11/20 03:59 AM
Headset in-use relay
by SST - 07/08/20 06:33 PM
Partner ACS AA
by mtncomm1 - 07/08/20 04:18 PM
Samsung SVMI20i
by crazy canuck - 07/08/20 03:40 PM
Help with Electra Elite IPK
by ECI Tech - 07/08/20 11:56 AM
Who's Online Now
37 members (dexman, Yoda, Carl Navarro, ffej010, RATHER BE FISHING, Mercenary Roadie, hitechcomm, hbiss, EV607797, nonameyet, newtecky, BobRobert, nortelvoip, justbill, mbhydro, usedphones, juno, Silversam, JBean3329, Marko65, Ruben, Rok1215, Arthur P. Bloom, Touch Tone Tommy, crazy canuck, Curlycord, OBT, KRRath, Memphisribs, mtncomm1, Bob-o, Joel J., Professor Shadow, jacktel, conxtel, Meyery2k, mike b), 320 guests, and 57 robots.
Key: Admin, Global Mod, Mod
Popular Topics (Views)
Forum Statistics
Forums94
Topics93,806
Posts636,323
Members49,310
Most Online5,661
May 23rd, 2018
Today's Birthdays
94astro, Jasonrod11, Joefish711, John McFerren, Timo
Newest Members
StevCom, DaleG, jlspeck, Real Estating, ForestHillChurch
49310 Registered Users
Get Tech Support Now! Click the banner below
Get Tech Support Now!
EMP & Lightning Home Surge Protection
EMP - Click Here!
Top Posters (30 Days)
dexman 21
dans 10
Bluewater Sailing
https://www.patreon.com/bePatron?u=5256033
EMP Shield for Commercial - Home & Vehicle
Use Coupon code SAVE - Click Here!
Servpro Ventura 24-Hour Emergency Service
Free Estimates call us now 24Hours
Contact Us | Telephone System Tech Support | Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers.
©Copyright Sundance Communications 1998-2020
Trusted Partners