love these customers.....
First, I am requested to run J hooks along the edge of the ceiling by the windows. We placed cat 32 J hooks every 4 feet. J hooks were setup as one J hook secured to beam with a second J hook piggbacked so that it looks like a giant "U". work is neat and professional.
Ceiling is white, wide open and plenum rated.
now the customer wants the "J" hooks to be covered up. I asked Caddy for support and they responded that they never heard of anyone covering up "J" hooks before.

So I am looking for a piece of thin white plastic (Plenum rated) that would wrap around the 2 J hooks and be easy to attach. I noticed that holes are drilled out on each of the J hooks so it should be easy to attach the plastic. the run is about 100 feet. any suggestions?

by the way the customer is an architectural firm.
Tj

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

#445283 03/13/07 03:41 AM
Joined: Feb 2005
Posts: 101
retired
retired
Joined: Feb 2005
Posts: 101
Why not just spray paint them the same color as the ceiling?


"Everyone needs something to believe in. I believe I'll have another beer"
#445284 03/13/07 03:56 AM
Joined: Dec 2004
Posts: 4,096
Member
*
Member
*
Offline
Joined: Dec 2004
Posts: 4,096
I grieve for you.

The thing about "architect's" is that they may be good at designing a building (note the word may) but they really have no care for how the mechanics of wiring works.

As for a fix are the hooks all in line (the holes) if so then why not a metal flashing like a gutter. In other words some 22 gauge flat flashing folded in a 90 then attached to the hooks

#445285 03/13/07 04:55 AM
Joined: Feb 2005
Posts: 12,354
Likes: 4
Member
***
Member
***
Offline
Joined: Feb 2005
Posts: 12,354
Likes: 4
Ceiling is white, wide open and plenum rated.

If it's wide open it's not a plenum or air handling space.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
#445286 03/13/07 05:14 AM
Joined: Jan 2006
Posts: 37
Member
Member
Offline
Joined: Jan 2006
Posts: 37
Why not give them a bright green stripe for accent like most architects would suggest for "asthetic" value!!
Seriously, I think paint them to match would be the best.

#445287 03/13/07 06:15 AM
Joined: Oct 2005
Posts: 116
Member
Member
Offline
Joined: Oct 2005
Posts: 116
Hal, where would I find more information on what determines a plenum or air handling space? I was told by the architects that this is a plenum space.
Tj

#445288 03/13/07 06:31 AM
Joined: Jan 2004
Posts: 6,648
RIP Moderator-Nisuko-Tie, General
*****
RIP Moderator-Nisuko-Tie, General
*****
Offline
Joined: Jan 2004
Posts: 6,648
seems like if open ceiling was considered plenum then everything in the bldg would need to be plenum

that plenum printer paper is really going to get expensive :rolleyes:


Skip
------------------------------------

Serving SW and West central Fl since 1984
#445289 03/13/07 07:39 AM
Joined: Feb 2005
Posts: 12,354
Likes: 4
Member
***
Member
***
Offline
Joined: Feb 2005
Posts: 12,354
Likes: 4
where would I find more information on what determines a plenum or air handling space?

NEC Article 100- Definitions

Plenum- A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.

See also:

Article 300.22(C) Other spaces used for environmental air.

This section applies to spaces used for environmental air handling purposes other than ducts and plenums... It does not include habitable rooms or areas of buildings, the prime purpose of which is not air handling.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
#445290 03/13/07 07:58 AM
Joined: Jan 2005
Posts: 15,395
Likes: 17
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,395
Likes: 17
Exactly!

If the hooks are visible, then they are clearly NOT within the confines of a plenum space unless clear panels are used as ceiling tiles.


Ed Vaughn, MBSWWYPBX
#445291 03/13/07 08:24 AM
Joined: Mar 2006
Posts: 378
Member
Member
Offline
Joined: Mar 2006
Posts: 378
I was wondering about the plenum thing myself. Why weren't the cables run above the ceiling (which would have actually been the plenum space)?


-Ken in MD-
www.kyawacomm.com
Page 1 of 3 1 2 3

Moderated by  Silversam 

Link Copied to Clipboard
Newest Topics
NEC IP Phones
by juno - 04/04/25 09:05 AM
NEC IP phones rebooting
by jpet621 - 04/03/25 03:03 PM
SV9100 store hours mailbox
by muddybl - 04/03/25 02:10 PM
Samsung Os 7400 Pri Caller Id No Info
by John807 - 04/02/25 06:19 PM
Forum Statistics
Forums84
Topics94,512
Posts639,933
Members49,844
Most Online5,661
May 23rd, 2018
Newest Members
yeloshak, ty3995, Sippy, sersmith, Taddeo
49,844 Registered Users
Top Posters(30 Days)
Toner 9
Taddeo 4
dexman 3
Who's Online Now
0 members (), 132 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998 - 2025
Powered by UBB.threads™ PHP Forum Software 8.0.0