Is it necessary to attach alternating support pedestals in each row of the raised floor to the bonding grid ,then alternate rows in an "S" fashion throughout the data center for proper grounding? Or can we simply run a perimiter loop with our #6 to alternating pedestals?
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Jan 2005
Posts: 15,395 Likes: 17
Moderator-Vertical, Vodavi, 1A2, Outside Wire
|
Moderator-Vertical, Vodavi, 1A2, Outside Wire
Joined: Jan 2005
Posts: 15,395 Likes: 17 |
No you don't have to do this. Since it's a continuous metallic structure, you only need to bond it one time and that can be through physical structural attachment to the building frame. You will need to check the UL listing for the flooring system to make sure that all interlocking parts qualify as electrically connected. Most of them are.
A piece of #6 copper between the raised floor frame system and the nearest I-beam is all that you need. Even that's overkill in my opinion.
I can't speak for particular local codes though, I'm just answering based upon the NEC. Local codes have a higher level of enforcement authority and I have heard that NYC is impossible unless you have a pocket full of Benjamins.
Try contacting our members "HBiss" or "SilverSam". They are mighty worldly on how things go on in NYC. Just use our directory feature in the upper-right corner of this page.
Ed Vaughn, MBSWWYPBX
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
Sam would be the one. I only know what I hear from across the County line. I was born there but I have very infrequently ventured back in the line of work. Not worth the hassel.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
I can't speak to the code as it's recently been revised and i don't have a current copy. I do believe it's available online though - call 311 and they should be able to give you the website.
Having said that - EVERY raised floor I ever worked on has been bonded numerous times. Every other pedestal & alternating rows sounds about right - but check for the latest revisions.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Sep 2006
Posts: 372
Member
|
Member
Joined: Sep 2006
Posts: 372 |
I believe the last one we had installed; the manufacturer had the grounding requirements to maintain the UL listing.