|
Joined: Aug 2005
Posts: 631
Member
|
Member
Joined: Aug 2005
Posts: 631 |
Currently working on a quote for a new school in Los Angeles. The specs clearly state they want service loops. 3 feet at the IDF and LDF and 10 at the MDF. Standard spec. But ... the plans show they want *all* CAT5 runs (v & d) run in conduit with no more than 2 per 3/4 inch. OK, so how do I give them service loops when the entire run is in conduit? And the plans lay out junction boxes too. I am assuming they want me to use standard steel boxes? Is that common? I've yet to do it that way. Now the thing is they have JBs being fitted with 3, 3/4 inch conduits for the runs to the walls but they have 1-1/2 inch conduit feeding the JB but I can only put 4 cables in a 1-1/2 as spec'd. The spec sheets only describe what kind of conduit they use in a conduit schedule, they do not say metal or plastic or flex duct or plastic flex duct. The plans do not specify plastic or steel. How would you quote that?
OK, it gets worse. There is a lot of fiber, 12 strand MM and 6 strand SM. They want me to also run the fiber through the same kind of junction boxes (same symbol on the plans) but that can't be done and maintain minimum bend radius which are included in the spec sheets.
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
The specs clearly state they want service loops. 3 feet at the IDF and LDF and 10 at the MDF. Standard spec. But ... the plans show they want *all* CAT5 runs (v & d) run in conduit with no more than 2 per 3/4 inch. OK, so how do I give them service loops when the entire run is in conduit?
It isn't in conduit at the IDF, LDF and MDF. Leave it coiled up at the rack.
I am assuming they want me to use standard steel boxes? Is that common?
Yes, this is commercial work, place of assembly. Are you the EC? I ask because why do you say that you will install the boxes.
Now the thing is they have JBs being fitted with 3, 3/4 inch conduits for the runs to the walls but they have 1-1/2 inch conduit feeding the JB but I can only put 4 cables in a 1-1/2 as spec'd.
Guess you are going to have to take that up with them.
The spec sheets only describe what kind of conduit they use in a conduit schedule, they do not say metal or plastic or flex duct or plastic flex duct. The plans do not specify plastic or steel. How would you quote that?
It's EMT, but again why do you ask? Are you going to install it?
No disrespect intended, but if you have to ask these questions why are you doing this? Most of what you ask are code issues which you should have knowledge of if you are going to do a job like this. -Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Aug 2005
Posts: 631
Member
|
Member
Joined: Aug 2005
Posts: 631 |
I assumed I'd have to leave it exposed but that sure is a lot of cable to leave out like that. Not being able to see this thing I am having a tough time visualizing it.
I am having trouble seeing why in some cases they treat the NEC like a bible verse and then they seem to override it with EIA/TIA but then they even break that spec. As I understand it, you are not supposed to supply more than four outlets per conduit. They have 6 outlets, 1 CAT5 per box rather than 4 boxes with say as many as 6 per box.
Lots of nearly empty conduit and not nearly enough copper to the stations. I suppose I am having trouble breaking through the massive over design in these city projects. All that money isn't buying much.
I'll have to hit the books again. We'll exclude all pathways in the bid.
|
|
|
|
Joined: Dec 2007
Posts: 2,033
Moderator-Toshiba
|
Moderator-Toshiba
Joined: Dec 2007
Posts: 2,033 |
I have to ask the same question as Hal...
Are you the EC?
If not, the EC should be the one to worry about/answer these questions and most likely, do the work.
If you are the EC, then you should have prior knowledge of these specs and be able to install accordingly, before bidding a job like this.
- Tony Ohio Data LLC Phone systems, data networks, firewalls and servers in Central Ohio. Some people aren't used to an environment where excellence is expected.
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
I am having trouble seeing why in some cases they treat the NEC like a bible verse and then they seem to override it with EIA/TIA but then they even break that spec.
The NEC is a minimum, anything that overrides it cannot be any less unless it is a local ammendment. Architect or engineer specs must at least be in accordance with the NEC and any local codes.
As I understand it, you are not supposed to supply more than four outlets per conduit. They have 6 outlets, 1 CAT5 per box rather than 4 boxes with say as many as 6 per box.
That's not from the NEC, probably a EIA/TIA spec. The EIA/TIA specs carry absolutely no regulatory weight and are only recommendations. These can be modified any which way however the architect or engineer wants.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Jun 2005
Posts: 512
Member
|
Member
Joined: Jun 2005
Posts: 512 |
It looks like we got us an EC.
|
|
|
|
Joined: Aug 2005
Posts: 631
Member
|
Member
Joined: Aug 2005
Posts: 631 |
No I am not the EC. We're bidding as a sub for C7 systems only. If I didn't ask these questions I would expect a few unhappy surprises come day 1 at the site.
|
|
|
|
Joined: Jun 2005
Posts: 102
Member
|
Member
Joined: Jun 2005
Posts: 102 |
Bring a copy of the NEC with you and ask where they get there info, as has been mentioned anything but the code book is nothing more than suggestions and or wants, or better yet check with the JHA that will be doing the final inspection.
Keep The Old Stuff Running
|
|
|
Forums84
Topics94,522
Posts639,996
Members49,851
|
Most Online5,661 May 23rd, 2018
|
|
1 members (EV607797),
255
guests, and
44
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
|