We have a need to identify specific fire / electrical / networking codes / regulations, etc that address the "standard" for installing a FIRE RATED back-board (i.e. fire resistant 3/4" plywood or 3/4" plywood with 2 coats of white fire retardant paint) behind wall-mounted IDF cabinets or on the walls in MDF closets. Any links / pointers to "authoritative" specifications for such are greatly appreciated!!
Thank You
Michael Schenck Director of Technology Konocti Unified School District
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
This would be a local code requirement and it varies from jurisdiction to jurisdiction. Most do not have this requirement, others do for certain occupancies and usually schools are one occupancy required to use them.
The place to start is the building inspector or fire marshal for the jurisdiction where the work will be done. He should be able to give you information where you can obtain the code sections with the information that you are looking for.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Dec 2002
Posts: 9,429 Likes: 3
Member
|
Member
Joined: Dec 2002
Posts: 9,429 Likes: 3 |
A lot of places have design standards where they will specify exactly what they require. UT has a section on their website that specifically outlines every detail of the cabling system as they expect it to be installed.
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
The ANSI/EIA/TIA Building Telecom Wiring Standards, Section 569-A Sub-Section7.2.4.1 states:
"A minimum of two walls should be covered with rigidly fixed 3/4" plywood....... either fire-rated or covered with two coats of fire retardant paint"
Please note that the EIA/TIA spec is NOT a code. It IS accepted by most architects, builders and major corporations as the gospel for Telecom Wiring Standards. Note that it says SHOULD and not SHALL.
Also please note that the version I am quoting from is NOT the most recent one. I do believe however, that if anything the spec has gotten more and not less strict.
As Hal said - GO TO THE AHJ (Authority having Jurisdiction) and get the definitive answer from them.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|