I read past posts, but couldn't find this specific info. I have a nightmare cable run to install through about 150 ft of flex conduit. The 1/8 in steel will not go through from either end.I found a break in the flex about 30 ft from one end where a previous installer broke the flex to negotiate two 90's-hopefully there are no more breaks cause we can't find any. Out here in the San Francisco area, almost noone uses conduit anymore, preferring Plenum cabling. Back in the good ole days in the phone company we used to carry a "big steel" for runs like these and very long runs. I can't remember if it was 1/4 in steel or 1/2 inch. Also, I've never used fiberglass fish tape. Would fiber be better for this run? I would assume it would be good for short distances but hard to force past 100 ft.
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: May 2002
Posts: 17,742 Likes: 34
Member
|
Member
Joined: May 2002
Posts: 17,742 Likes: 34 |
Providing no more breaks a vacuum might be the easiest method.
Retired phone dude
|
|
|
|
Joined: Apr 2004
Posts: 585
Member
|
Member
Joined: Apr 2004
Posts: 585 |
Unfortunately there are 2 cables in the conduit which would interfere w a seal. The tech onsite said these cables wouldn't budge to use a a pull wire and then pull them back in.
|
|
|
|
Joined: Feb 2005
Posts: 12,354 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,354 Likes: 4 |
The most important part of the information you left out- what size is the conduit and what is it? Greenfield (FMC), Sealtite (LMC), plastic?
None of those are suitable for 150' runs so basically you are screwed even with nothing in it. Depending on the size, if it were me I would try a 1/8" tape with a spring leader but I wouldn't get my hopes up. There has to be some reason the existing runs can't be pulled out and that right there isn't good news.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
150' is too long a run to be installed with flex. Perhaps there's a pull box in the middle of the run (at the 100' mark) and that's why you can't pull the old cables out?
It's also possible that the old cables were installed with a crappy lubricant which has dried and hardened.
The fish snake you're remembering was probably a 1/4" one.
You might get better results with a rodder, but - as Hal said - How big is this conduit? What size are the cables already in it?
Why don't you just pull the new run in plenum and bypass the conduit?
Bill, I've never had any luck with a vacuum on flexible conduit (Greenfield) - too much air loss.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Dec 2002
Posts: 341
Member
|
Member
Joined: Dec 2002
Posts: 341 |
I've seen a number of Greenfield runs where the sparkies convoluted the flex so much you couldn't get anything through it. We've done some installations where we actually pull our cables through before the electricians finalize the placement. Here's one example of why we always pull a follow-line in with our cables for (possible) future use.
Also, I second Sam's analysis of air loss for a vacuum install.
Bill
|
|
|
|
Joined: Dec 2004
Posts: 5,722
Member
|
Member
Joined: Dec 2004
Posts: 5,722 |
I think Sam pretty well called it although I wouldn't count out the vacuum trick...or blowing. Yep, probably a box somewhere. Blow and listen for the whistle.
I have a 1/8th inch fiberglass tape (125') that is like pushing a wet noodle but it will go places no other tape will go....it works well with flex.
Good Luck.
Ken ---------
|
|
|
|
Joined: Dec 2005
Posts: 2,928
Member
|
Member
Joined: Dec 2005
Posts: 2,928 |
ken may be onto something....maybe a softsnake
I Swear I did not touch anything
|
|
|
|
Joined: Dec 2006
Posts: 106
Member
|
Member
Joined: Dec 2006
Posts: 106 |
I have had good luck with a rigid fiberglass snake, it wasn't cheap, I think it was $150 for 100'
|
|
|