I'm planning on each conduit drop for new building construction to have 4 cables and 4 jacks: 2 - Cat 6a with cat 6 jacks,and 2 - Cat 5e with cat 5e jacks.
I expect I should use a 1 inch conduit from the ceiling down to the box. Not sure if a 90 degree sweep will be used or not.
The box should be what I call a "4 square" box, with a single gang reducing mud ring. What dimension for depth of the box?
Do these sound right? Thanks.
Jim
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Dec 2002
Posts: 9,429 Likes: 3
Member
|
Member
Joined: Dec 2002
Posts: 9,429 Likes: 3 |
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: Oct 2006
Posts: 1,417 Likes: 7
Member
|
Member
Joined: Oct 2006
Posts: 1,417 Likes: 7 |
That's a great paper Jeff, no matter which brand a guy uses.
I like the idea of using angled wall plates, with no 90 degree sweep above. Just push excess slack loop back up the 1" conduit.
Thanks Jeff.
Jim
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
Nicely done, Jeff, that's an excellent doc.
Yoda, stop by an electrical supply house and check availability and pricing of extra-deep boxes. An alternative is also a 4&11/16" box (sometimes called a 5" box). They're available in a standard depth but being wider can provide a little more "wiggle" room. They have their own single gang mud ring.
Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Oct 2006
Posts: 1,417 Likes: 7
Member
|
Member
Joined: Oct 2006
Posts: 1,417 Likes: 7 |
Reading the Hubbel doc that Jeff mentioned, they show lots of angled faceplates. I never used them, but it makes sense.
They also recommend not putting any slack loop in the box, but pushing the slack up the conduit and leaving it in the ceiling. With cat 5e, I always put a small loop inside the box, and it fit ok. Won't be able to do that with 6a.
Jim
|
|
|
|
Joined: Nov 2008
Posts: 627
Member
|
Member
Joined: Nov 2008
Posts: 627 |
If you don't need a fire/sound rating, you could use an open back box with a conduit "tab" on the top and bottom. If you need something enclosed, Raco makes 4 square boxes at least 2 1/8" deep, and mudrings at least 2" deep. We use the deep boxes for cat6 and coax, and the rings are usually 1 1/4" for double layer drywall/soundboard-drywall.
The 2 1/8" deep boxes cost almost 3x as much as the standard 1 1/2" deep boxes, and a 7 x 7" putty pad will not completely cover one (more $$$).
Havent worked with much 1 or 1 1/4" EMT - are boxes readily available with those sized knockouts, or do they have to be punched to size?
Jack
The question is more important than the answer.
|
|
|
|
Joined: Oct 2006
Posts: 1,417 Likes: 7
Member
|
Member
Joined: Oct 2006
Posts: 1,417 Likes: 7 |
I think I'm going with the Raco 4 square 2 1/8" deep box with 1" knockouts.
Thanks for all the suggestions. Jim
|
|
|
|
Joined: May 2007
Posts: 5,059 Likes: 6
Moderator-1A2, Cabling
|
Moderator-1A2, Cabling
Joined: May 2007
Posts: 5,059 Likes: 6 |
Originally posted by Fletcher: Havent worked with much 1 or 1 1/4" EMT - are boxes readily available with those sized knockouts, or do they have to be punched to size?
Jack Can't speak for HD or Loewes but Electrical Supply Houses should have at least the 1" in stock. I've certainly used 1.25" often on jobs (usually for Voice & Data). Sam
"Where are we going and why are we in this hand basket?"
|
|
|
|
Joined: Nov 2006
Posts: 193
Member
|
Member
Joined: Nov 2006
Posts: 193 |
Yoda I do a lot of 3/4 Emt you can fit up to 6 cat 5 or 4 cat6 cables. Juno
|
|
|
|
Joined: Dec 2004
Posts: 5,722
Member
|
Member
Joined: Dec 2004
Posts: 5,722 |
Gentlemen, we need to get our RCDD guys to respond....BUT....the box must support the number and size of the conduits. That dictates the box size while the fill rate dictates the conduit size. A=B+C....  :read: :idea: