Yes, the feeds are Cat5e, unshielded and unbonded. The electrical inspector will not write up a violation on this simply because "it's low voltage, and we don't inspect low voltage."
The RG6 will not make it over that distance. But Sparkie thinks it's OK.
I have been called in on many, many auto gate jobs where the gates acted flaky. The culprit every time was the proximity of the signal cable and the power cable.
When the gate starts to open, the EMF pulse in the 110 line creates a blip on the signal cable, and the gate stops opening (or closing) and goes the other direction, or goes half way, and reverses again, or stalls completely.
Putting an unshielded Cat5e from the house to the gate, right next to the UF cable, will cause this havoc.
My recommendation is not to put the signal and power even in the same trench. Separate them by at least a foot, and always use BSW, properly bonded and grounded, for the signal cable.
Arthur P. Bloom "30 years of faithful service...15 years on hold"
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Feb 2005
Posts: 12,356 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,356 Likes: 4 |
The electrical inspector will not write up a violation on this simply because "it's low voltage, and we don't inspect low voltage."
Low voltage outside of the premises doesn't fall under the NEC so there is nothing for the inspector to inspect.
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Sep 2006
Posts: 3,290
Member
|
Member
Joined: Sep 2006
Posts: 3,290 |
Maybe I've been misinformed, but I believe that the method of bonding the entrance cable is covered by the NEC. No shield, therefore no bond, therefore a violation.
Arthur P. Bloom "30 years of faithful service...15 years on hold"
|
|
|
|
Joined: Feb 2005
Posts: 12,356 Likes: 4
Member
|
Member
Joined: Feb 2005
Posts: 12,356 Likes: 4 |
I believe that the method of bonding the entrance cable is covered by the NEC
Yes, 800.22
-Hal
CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
|
|
|
|
Joined: Nov 2008
Posts: 627
Member
|
Member
Joined: Nov 2008
Posts: 627 |
Arthur, what happened with sparkie?
Jack
The question is more important than the answer.
|
|
|
|
Joined: Sep 2006
Posts: 3,290
Member
|
Member
Joined: Sep 2006
Posts: 3,290 |
Sparkie, he mad now, boss.
Me bring big spools coax and BSW.
Me install in trench.
Me bring into building and rip out Sparkie wire.
Him complain to GC.
GC tell Sparkie too bad, Phone Man know what he doin' and you don't.
Arthur P. Bloom "30 years of faithful service...15 years on hold"
|
|
|
|
Joined: Nov 2008
Posts: 627
Member
|
Member
Joined: Nov 2008
Posts: 627 |
Originally posted by Arthur P. Bloom: Sparkie, he mad now, boss.
Me bring big spools coax and BSW.
Me install in trench.
Me bring into building and rip out Sparkie wire.
Him complain to GC.
GC tell Sparkie too bad, Phone Man know what he doin' and you don't. :rofl: Love the ogre talk, too. So easy a caveman can do it (but not a sparkie!) Jack
The question is more important than the answer.
|
|
|
|
Joined: Sep 2006
Posts: 3,290
Member
|
Member
Joined: Sep 2006
Posts: 3,290 |
Actually, I was aiming at Jamaican, but I can see where you might think it's Cave Man.
Arthur P. Bloom "30 years of faithful service...15 years on hold"
|
|
|
|
Joined: Dec 2002
Posts: 9,429 Likes: 3
Member
|
Member
Joined: Dec 2002
Posts: 9,429 Likes: 3 |
I love it when a plan comes together!
Jeff Moss Moss Communications Computer Repair-Networking-Cabling MBSWWYPBX, JGAE
|
|
|
|
Joined: Dec 2005
Posts: 7,056
RIP Moderator-Mitel, Panasonic
|
RIP Moderator-Mitel, Panasonic
Joined: Dec 2005
Posts: 7,056 |
" So easy a caveman can do it (but not a sparkie!)" -------------------------------------------------
:rofl:
When I was young, I was Liberal. As I aged and wised up, I became Conservative. Now that I'm old, I have settled on Curmudgeon.
|
|
|
Forums84
Topics94,525
Posts640,013
Members49,852
|
Most Online5,661 May 23rd, 2018
|
|
0 members (),
284
guests, and
43
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
|