I work at a small college that has a Contel Executone 3672 phone system installed. It's been there since the early 90's. This morning, all the phones in the building started ringing at the same time. When you pick up the handset all you hear is a lot of "high-voltage" static. I have reset the system several times, cleaned the various components, etc. but nothing has worked. Everytime I turn the system back on, all the phones start ringing continuously. My question is this: What's the best way to troubleshoot my problem? Should I be looking at replacing the ring generator unit or the DC/DC Converter or something else? Any help on this would be greatly appreciated.

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Feb 2005
Posts: 1,037
Member
Offline
Member
Joined: Feb 2005
Posts: 1,037
My guess would be the DC/DC Converter. It's been so long...someone else will jump in and I will grab my book when I get home tonight and check back.

Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
The DC/DC converter has test points on the front face. Check them with a good digital voltmeter. The +5 volts DC is perhaps the most likely culprit since it affects the processor and IC's directly. I seem to recall that there is a screw-type adjustment that can be made but please be very careful in turning it, as in fractions of a tick while you watch the meter. If anything, try adjusting it downward first to get a feel for the sensitivity of the adjustment process.

If that doesn't have any positive effect, chances are that you will need a new DC/DC card. That's about the only thing that fails in those systems and it's usually due to excessive heat. You may also want to try leaving the cover off and even pointing a fan toward it to see if there's any change in behavior. Fortunately, I don't think you will have too much trouble locating a replacement since that was quite a popular system.


Ed Vaughn, MBSWWYPBX
Joined: Sep 2007
Posts: 9
Member
OP Offline
Member
Joined: Sep 2007
Posts: 9
I metered the front test points and I'm getting 3.8 v on both the +5 and +14 ports. When I try to change the +5 adjustment screw, there is no change whatsoever in the voltage reading at either test point. I'm assuming from this that the DC/DC board is shot. I guess I'll check ebay.

Joined: Jan 2005
Posts: 15,378
Likes: 13
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Offline
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,378
Likes: 13
Please don't check e-bay for something like this. PM sent.


Ed Vaughn, MBSWWYPBX
Joined: Sep 2007
Posts: 9
Member
OP Offline
Member
Joined: Sep 2007
Posts: 9
I have a new DC/DC converter installed and still have a problem. When I turn the system on and meter the test points, I'm getting 14v on the +14v test point, but only 2.2-3.6v on the +5v test point. Is this correct? Turning the adjustment screw causes all the relays in the system to click like crazy and then the +5v led gets real dim. Maybe something else could be the problem? Any help would be greatly appreciated.

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Online Content
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
I would say that is out of tolerance, in skimming through the manual I didn't find the tolerances. It looks like you got the plus 14, I think I'd put a meter on it and start pulling packs to see what's dragging it down. Do all your testing from the blocks so as to eliminate any possible cable problems. Your voltage should be close to 5.


Retired phone dude
Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Online Content
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
Found the tolerances in section 801, your only allowed 1%, which would be about .5volts. I'd check them all while your at it to see if everything in within specs.


Retired phone dude
Joined: Sep 2007
Posts: 9
Member
OP Offline
Member
Joined: Sep 2007
Posts: 9
I just detached the ring generator unit and now the system meters perfectly. I'm thinking a power surge may have damaged the RGU. Sound possible?

Joined: May 2002
Posts: 17,722
Likes: 18
Member
****
Online Content
Member
****
Joined: May 2002
Posts: 17,722
Likes: 18
Anything is possible, that's why I suggested what I did. See if other features are working without the ring generator.


Retired phone dude
Page 1 of 3 1 2 3

Moderated by  nonameyet, pvj 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics94,262
Posts638,697
Members49,757
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
211,100 Shoretel
187,712 CTX100 install
186,800 1a2 system
Newest Members
BPopilek, Rich F, LewisR, TDKs79, Buttinset
49,757 Registered Users
Top Posters(30 Days)
dexman 18
Toner 11
TDKs79 8
teleco 4
Who's Online Now
0 members (), 140 guests, and 24 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998-2024
Powered by UBB.threads™ PHP Forum Software 7.7.5