I know this topic has been discussed ad nauseum in other forums, but I can't seem to nail down a specific topic that covers what I need (Search is not my friend today).

I'm looking for documentation showing specific requirements regarding sinking your own ground rod for grounding racks and other telecom/data equipment. My recollection is that the separate rod needs to be bonded to the electrical panel or ufer to prevent potential between the ground rod and the ground that's on the energized equipment mounted in the rack.

Can someone please straighten me out, with reference to code (electric, BICSI, etc.)?

Thanks!

Justin

Joined: May 2002
Posts: 17,671
Likes: 5
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,671
Likes: 5
This topic was posted a long time ago, but I believe it's still relevant.

Common bond was in the Bell System Practices, I'm not sure what all BICSI copied over, I know they did a lot of it, but all that could have changed. I'm not at all familiar with BICSI Standards. I would think common bond is still a followed practice. To me it's just common sense to have no difference in potential in the grounds.

EDIT: To add, I don't recall common bond ever being in the NEC.


Retired phone dude
Joined: May 2007
Posts: 5,021
Likes: 2
Moderator-1A2, Cabling
*****
Offline
Moderator-1A2, Cabling
*****
Joined: May 2007
Posts: 5,021
Likes: 2
Grounding & Bonding is covered extensively in EIA/TIA 607 spec. Unfortunately my copy of the spec is OLD (20th Century).

Google EIA 607 you should find plenty of good info.

Sam


"Where are we going and why are we in this hand basket?"
Joined: May 2002
Posts: 17,671
Likes: 5
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,671
Likes: 5
So did BICSI adopt the ANSI Standard in it's entirety? I did know they adopted parts.

Good info Sam.


Retired phone dude
Joined: Jun 2001
Posts: 10,949
Moderator-Avaya
*****
Offline
Moderator-Avaya
*****
Joined: Jun 2001
Posts: 10,949
I was always tought the same as Bill, all grounds should be bonded to building or common ground.


Avaya SMB Authorized Business Partner. ACIS/APSS
ESI Certified Reseller/Installer
www.regal-comm.com
Joined: Jun 2004
Posts: 4,550
Moderator-Comdial, ESI, Voicemail, Cisco
OP Offline
Moderator-Comdial, ESI, Voicemail, Cisco
Joined: Jun 2004
Posts: 4,550
Thanks! The link https://www.psihq.com/iread/strpgrnd.htm provides pretty clear reference. If you're following NEC guidelines only, it would be enough to tell you my understanding is correct. I was challenged by a "fact" that BICSI did not speak to the need for bonding supplemental grounds to the building grounding system, and that BICSI was over and above anything the NEC said. If BICSI doesn't speak to it, it should for this very reason.

Justin

Joined: May 2002
Posts: 17,671
Likes: 5
Member
****
Offline
Member
****
Joined: May 2002
Posts: 17,671
Likes: 5
So that tells me BICSI didn't adopt all the ANSI standards.



Retired phone dude
Joined: May 2007
Posts: 5,021
Likes: 2
Moderator-1A2, Cabling
*****
Offline
Moderator-1A2, Cabling
*****
Joined: May 2007
Posts: 5,021
Likes: 2
Justin -

The NEC covers Grounding and Bonding from a SAFETY standard.

BICSI, EIA/TIA/ANSI cover Grounding and Bonding from a PERFORMANCE standard.

B I G difference.

Grounding in the era of Steppers, XBar, 1A2 and the like was a lot easier then now. 2 or 3 volt imbalance won't effect a 1970 era phone system. But a "modern" VOIP system? It would hose it.

I worked for a company that was contracted by NBC to provide Telephone service to the Olympics in Russia (1984?). We opted to provide a XBar, because the question was raised whether a "new" electronic system (NEAX 22L) would function with the poor quality Russian infrastructure. Grounding was a major concern. Of course, because of Afghanistan we never got to do the job.


Sam


"Where are we going and why are we in this hand basket?"
Joined: Jun 2004
Posts: 4,550
Moderator-Comdial, ESI, Voicemail, Cisco
OP Offline
Moderator-Comdial, ESI, Voicemail, Cisco
Joined: Jun 2004
Posts: 4,550
Although the wording isn't very clear in EIA 607, it does say the same thing.

Justin

Joined: Nov 2011
Posts: 320
Member
Offline
Member
Joined: Nov 2011
Posts: 320


Here is a video from Mike Holt, this is talking about CNC machines but same would apply to any of our non-electromagnetically/digital equipment.

See the diagram at 15:00 for the quick explanation.


Moderated by  EV607797 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics93,378
Posts634,603
Members49,525
Most Online5,661
May 23rd, 2018
Popular Topics (Views)
Today's Birthdays
djone21, glacier37, Supert8ch
Newest Members
NiagaraGuy, Luv2uallday, FredSkidoo, tspa, xtrememachines
49,525 Registered Users
Top Posters (30 Days)
Toner 20
dexman 10
R4+Z 6
Who's Online Now
0 members (), 16 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: Business Telephone Systems Canada | Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers.
©Copyright Sundance Communications 1998-2022
Powered by UBB.threads™ PHP Forum Software 7.7.5