Greetings,
I'm not sure why but lately I've come across a lot of systems installed above drop ceilings. It's obvious they were installed after the ceiling was installed some as high as 12 feet. What I'm looking for are any national codes prohibiting the practice. So far the only one I can find from NEC is that no flexible cords may be plugged into an outlet above a drop ceiling that is 400.7 I believe. I also thought there was a code about equipment being installed at a workable height and clearance? These clients think I'm nuts when I tell them before I work on it I have to move it. The general response is whatsa matter ain't you got a ladder?
Thanks


John 807
Atcom VoIP Demo
VoIP Demo
Joined: Dec 2012
Posts: 252
Member
*****
Offline
Member
*****
Joined: Dec 2012
Posts: 252
Just shotgunning this but from what I understand of the NEC, only Class 2 power supplies (that are plenum rated, good luck finding that...) can be installed above the ceiling. This would rule against the flexible cords as mentioned. This link explains the reasoning behind this. Interestingly, it is not because there is 120VAC in the cable but the simple reason that the electrical cable is not plenum rated.

Unfortunately, if it is after the fact, it will probably never be picked up on a fire inspection because the inspector probably "ain't you got a ladder" either.

https://ecmweb.com/low-voltagecommunications/what-lurks-ceiling


Last edited by Meyery2k; 01/26/16 05:43 PM.

Michael Meyer
Joined: Dec 2007
Posts: 6,755
Likes: 11
Retired Admin
*****
Offline
Retired Admin
*****
Joined: Dec 2007
Posts: 6,755
Likes: 11


Dean
Photographs:
https://www.instagram.com/deanwilsoncanby/
https://fstoppers.com/profile/deanwilsoncanby
https://www.facebook.com/Dean-Wilson-Photography-112841337020414

Please don't confuse your "Internet Search" with my licenses, certifications and over 30 years experience.

"Thank you for calling Technical Support. If you feel you have reached this number in error, please hang up and press redial."
Joined: Feb 2005
Posts: 12,334
Likes: 3
Member
***
Offline
Member
***
Joined: Feb 2005
Posts: 12,334
Likes: 3
It's not unusual to install equipment above a dropped ceiling. Alarm panels and access control panels come to mind. But the thing is that with them they are powered remotely by a low voltage transformer plugged into a receptacle that is not within the ceiling space. With a phone system you are going to have a problem. As far as I know the only thing the NEC says is if the system is installed there you can't plug it in. You can't connect it to a receptacle installed above a dropped ceiling nor can you run the line cord through a hole in the tile to a receptacle below.

That said, the building code may have something else to say especially if the space above the ceiling is used for environmental air.

-Hal


Moderated by  ChrisRR, EV607797, Silversam 

Link Copied to Clipboard
Forum Statistics
Forums84
Topics93,879
Posts637,000
Members49,673
Most Online5,661
May 23rd, 2018
Popular Topics(Views)
Today's Birthdays
cindysue, esibole1, jpblock82
Newest Members
APInc, m1cashman, jonnycom, XJR9000, BitBang
49,673 Registered Users
Top Posters(30 Days)
Toner 11
teleco 6
dexman 5
jsaad 5
Shahza 4
tim10 4
Who's Online Now
0 members (), 26 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: Business Phone Systems | Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers.
©Copyright Sundance Communications 1998-2023
Powered by UBB.threads™ PHP Forum Software 7.7.5