HI! Again , quick question to the pros if the building electical goes to main water pipe and i am 120 ft. away from main ground, can i find a closer water pipe to run a # 6 gound for the circa protection?? Or do i have to run a large cooper wire to main ground in electrial room??The building trusses are not grounded. eek

Atcom VoIP Phones
VoIP Demo

Best VoIP Phones Canada


Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.

Joined: Feb 2005
Posts: 12,360
Likes: 4
Member
***
Member
***
Offline
Joined: Feb 2005
Posts: 12,360
Likes: 4
Drive an 8'x5/8" ground rod at the protector location. From the protectors and that ground rod run a #4 copper ground conductor back to the electrical room.

-Hal


CALIFORNIA PROPOSITION 65 WARNING: Some comments made by me are known to the State of California to cause irreversible brain damage and serious mental disorders leading to confinement.
Joined: Jan 2005
Posts: 15,409
Likes: 18
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Moderator-Vertical, Vodavi, 1A2, Outside Wire
*****
Joined: Jan 2005
Posts: 15,409
Likes: 18
Well, I'm not sure of the Canadian Electrical Code requirements, but I'm fairly confident that they are similar to those in the US.

IF, (and I mean that you will need to confirm this) there is a 3/4" or larger copper cold water pipe that is not insulated by some form of joint or plastic piping, you will be OK. Don't forget to check for plastic water meter housings. This pipe will be a superior bonding connection to steel building framing anyway.

Otherwise, proper integrity over such a distance would require something more like a #2AWG bond to go all the way to the electric service ground. This would be necessary to overcome resistance due to distance. The proper water pipe will save you this trouble and expense.

Still, it concerns me that the metal framing members are not bonded to the electric, water and gas (if present) facilities. You might want to double-check that and if it truly is the case, you should advise the building owner of this deficiency.


Ed Vaughn, MBSWWYPBX
Joined: Nov 2006
Posts: 715
Member
Member
Joined: Nov 2006
Posts: 715
Thanks guys,i did talk to the original electric contractor and he did confirm the the steel beam trusses are not grounded ,this is a 1 yr. old building, So if i can find cooper piping with no non conductor joints a can use this as the cheapest solution.?? Thanks

Joined: Dec 2004
Posts: 5,722
KLD Offline
Member
Member
Joined: Dec 2004
Posts: 5,722
Watch yourself if the building is not grounded or bonded....not even cathodic protection. You don't want to become the better ground.


Ken
---------
Joined: Sep 2007
Posts: 1,173
Member
Member
Joined: Sep 2007
Posts: 1,173
75% of the OSP enclosures and 90% of the data racks I see here are not grounded at all.

Trying to put together a 'grounding kit' right now so we have what we need on hand at any job, hopefully. Can't depend on, or wait for, a sparkie to provide a ground.

Joined: May 2007
Posts: 5,059
Likes: 6
Moderator-1A2, Cabling
*****
Moderator-1A2, Cabling
*****
Joined: May 2007
Posts: 5,059
Likes: 6
Noisycow -

Recognize that there are 2 kinds of grounding:

1 - for safety
2 - for performance

For safety related grounding refer to the NEC

For performance related grounding refer to the EIA/TIA 607 spec. Panduit also has a nice set of grounding equipment and practices for data centers and the like.

Sam


"Where are we going and why are we in this hand basket?"

Moderated by  EV607797 

Link Copied to Clipboard
Newest Topics
Tone / Probe repair
by jsaad - 07/02/25 03:49 PM
TDE-100 and KX_NT533 phones
by Jeb67 - 07/01/25 06:41 PM
SPNET "blocking"?
by CyberLaw - 06/30/25 10:47 AM
Forum Statistics
Forums84
Topics94,562
Posts640,147
Members49,863
Most Online5,661
May 23rd, 2018
Newest Members
1A2, Christian Center, Zach8789, tectrolink, mcgyver
49,863 Registered Users
Top Posters(30 Days)
Toner 12
C5Z 3
dexman 2
SamF 2
Who's Online Now
0 members (), 56 guests, and 37 robots.
Key: Admin, Global Mod, Mod
Contact Us | Sponsored by Atcom: One of the best VoIP Phone Canada Suppliers for your business telephone system!| Terms of Service

Sundance Communications is not affiliated with any of the above manufacturers. Sundance Phone System Forums - VOIP & Cloud Phone Help
©Copyright Sundance Communications 1998 - 2025
Powered by UBB.threads™ PHP Forum Software 8.0.0