Hello, last week I removed a Toshiba Strata CTX28 from a location we were closing and reinstalled it in a location where the old Panasonic system had been failing ( some extensions didn’t work, voicemail was only working when it wanted too etc.). I have some experience with Mitel, older partner and Merlin phone systems so using Winadmin I was able to adapt the system programming to the current location. The voice mail and system attendant setup also went ok. I would like to set some stations to delayed ringing and restrict some extensions from dialing outside but, those are future goals.
The problem I am having is getting the system to open an electric strike for a door.
There is no phone at the door; it’s a simple 24 volt circuit that is normally open and closing the circuit with a button or relay energies the solenoid. The wires are mounted on the screw down terminals under the MOH RCA jack in the cabinet. I have read through the programming and installation manuals and did a search on this forum but still can’t seem to get it to work.
In form 104 field 12 (door unlock timer) I left the default of 6
In form 508 (door lock control) field 00 I selected 1 from the drop down menu for the door lock # . In field 01 I selected BIOU for the interface type. In field 3 relay number I selected 1 from the drop down menu.
In form 515 BIOU (control relay assignments) field 00 (labeled BIOU 1 or 2) I selected 1 from the drop down menu . In field 01 I entered “DOOR LOCK†I believe I had to type this in.
In form 205 I assigned a key for door unlock (door # 1) to a station. I also tried dialing #12 from the phone.
Am I missing a step someplace ? As I am not that familiar with the Winadmin software or the CTX28 system configuration newbie friendly help would be appreciated. Unfortunately calling in a distributor isn’t an option at this time because of financial concerns.
Thanks in advance.
|
|
|
Visit Atcom to get started with your new business VoIP phone system ASAP
Turn up is quick, painless, and can often be done same day.
Let us show you how to do VoIP right, resulting in crystal clear call quality and easy-to-use features that make everyone happy!
Proudly serving Canada from coast to coast.
|
|
|
Joined: Aug 2009
Posts: 4
Member
|
Member
Joined: Aug 2009
Posts: 4 |
I found the answer to this.
in form 508 field 3; the relay # should be set to 5 just like the CTX100. The manuals all mention this setting for the CTX 100 but do not say anything the CTX 28
|
|
|